Solar power usage for a 500ltr fridge over 24hours
Submitted: Monday, Sep 12, 2005 at 18:44
ThreadID: 26392 Views:3870 Replies:10 FollowUps:21
Hi there,
I have a solar setup - very basic (6*T105's [12 single qty] @ 12volts), and i was wondering what i was actually getting per day in AMPS. A very nice fellow sent me this link; http://members.dodo.com.au/~landline/solarhours/index.html
Which is a good guide. So i measured by physically checking from 09:00 till 13:00 [6 hours] getting a good 10amps, then dropping off etc - so basically i was getting, lets say for arguments sake, 80 - 100 amps in a day.
I measured a 2000W 240volt = 8amps kettle, and my inverter showed [150amps at 12volts to power it]. Please tell me if i am wrong in that, i'm running around with my tail between my legs at the moment with all this.....
So, my 500ltr fridge (which has 1Amp on the power sticker). Seemed [As indicated on the 3000w modified inverter], to have a start up current of 1600w (compression phase), and then settling down to 300-440w (normal ticking over requirements?), didn't have the time to watch it all though, with the kids and my loving wife :)
I'm getting myself really confused now guys.....
So, basically, can i run the fridge - assuming my current battery supply at dusk, is reading 12.00volts [Inverter cut off at 11vlts] - through the night, then starting to be topped up at say 06:00 hours?
Last question:
If 4 * 80 watt panels = 20amps. Then 8 * 80W = 40maps.
But if have one 40amp capable carrying cable, what do i do, if i only have 2qty 20amp solar regulators?
So if i have 1 cable chucking down 40amps; if i split the cable into half and put one half into one 20amp reg and the other visa versa - hopefully splitting the amperage - would that be ok?
You can split and add ohms and capacitence - via series and parrallel - why not Amps?
Ok. Have have to go, teas up i hear :(
Have to wait for morning, but i'll try and slink in later :)
Thanks,
Alan.
Reply By: Nudenut - Monday, Sep 12, 2005 at 18:50
yes you can run two cables to allow cable to draw approx 1/2 thru each
AnswerID: 129722
Reply By: Footloose - Monday, Sep 12, 2005 at 18:52
I'm missing something here...a 500ltr fridge ? Must be a big boat ?
AnswerID: 129723
Follow Up By: Muddy 'doe (SA) - Monday, Sep 12, 2005 at 19:15
Same here,
would there be room for anything else???
FollowupID: 384184
Reply By: Wok - Monday, Sep 12, 2005 at 20:10
Alan,
Sounds like you are running 2 seperate systems[each 4x80watts+20A regulator] in parallel to 1 battery bank?
Are the regulators that closely matched in output voltage to allow this mode?
AnswerID: 129746
Reply By: avro - Monday, Sep 12, 2005 at 20:17
Alan.
First off an "AMPS" measurement is an instantaneous reading. Amp hours are the measure we need to use here ie 10 amps for an hour is 10 amp hours. So you are getting 80 to 100 amp hours per day out of your solar cells.
To run a 2000 watt kettle of 12 volts via an inverter could use up to 200 amps (or if it takes 10 minutes to boil 200/6 = 33 amp hours.
If your fridge draws 440 watts then you are looking at a current draw off 12 volts of around 40 amps. So if it runs continuously for an hour, thats 40 amp hours gone.
So if you are putting 80 to 100 amp hours in, thats about 2 hours of fridge running continuously (I know, I know they dont run continuously) or 3 hours of kettle boiling.
I find a rough rule of thumb for determining current draw through an inverter is to divide the 240 volt watts by 10 ( ie divided by 12 with an allowance for losses in the inverter).
Hope this helps
AnswerID: 129748
Follow Up By: Mainey (WA) - Monday, Sep 12, 2005 at 22:37
Different types of "inverters" have different power outputs and self consumption figures...
but that is a whole new ball game and whatever will be written someone else will condem it without offering their reasons or their own answer.
Then there are some who have a fridge powered by a 12v battery
that utilises a 240v compressor
but it does NOT use an inverter :-)
but that's technology
it's beyond the belief of some
and above the understanding of many!
FollowupID: 384217
Follow Up By: Breadman - Tuesday, Sep 13, 2005 at 06:42
"but it does NOT use an inverter :-)" LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL oh dear the incorrect information posted here is laughable but tragic
FollowupID: 384235
Follow Up By: Mainey (WA) - Tuesday, Sep 13, 2005 at 11:07
(QUOTE) but that is a whole new ball game and whatever will be written someone else will condemn it "WITHOUT" offering their reasons or THEIR own answer (end quote)
The only thing that is "tragic" and "laughable" is that Breadman is living back in the OLD electronics technology, he is very obviously unaware of what advances are being made in electronic technology this century (21st Century)
breadman, please state what you believe is incorrect ??
.....OR.....
is it simply that you really don't understand the new TECHNOLOGY :-)
It’s a now fact of life, due to new electronics technology available, a 240v fridge compressor can be run off a 12v battery, WITH-OUT an inverter.
No, the 12v battery does NOT "directly" run the 240v compressor!
BUT as I said, it does NOT run from an inverter!!
I repeat there is.... NO INVERTER used in the fridge
Yes, they do exist and in the form as I have posted – without inverter!
The electronics are so technologically advanced, that breadman is obviously totally UNAWARE of what is available today, otherwise he would not make ridiculous statements that are factually incorrect (as in ..wrong)
He who laughs last, laughs loudest!
LOL LOL LOL LOL Ozi LOL LOL LOL LOL LOL Ozi LOL LOL LOL LOL
the "T" model Ford was once an unreal NEW vehicle, that however is old technology, now we have BATTERY powered cars in this the 21st Century.
FollowupID: 384272
Follow Up By: Breadman - Tuesday, Sep 13, 2005 at 11:26
you must be the king and queen of wrong and misinformation
"It’s a now fact of life, due to new electronics technology available, a 240v fridge compressor can be run off a 12v battery, WITH-OUT an inverter." LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL oh dear the incorrect information posted here is laughable but tragic
FollowupID: 384277
Follow Up By: Mainey (WA) - Tuesday, Sep 13, 2005 at 11:49
(QUOTE) It’s a now fact of life, due to new electronics technology available, a 240v fridge compressor can be run off a 12v battery, WITH-OUT an inverter.
BUT as I said, it does NOT run from an inverter!! (end quote)
Read it as it is printed and you will see it says an inverter is not used!
However..... the method of converting the power from 12v up to 240v is NOT mentioned, but only implied.... and I repeat, it's NOT called an inverter!!!!
Just because you are NOT up to date on modern electronics technology and are totally unaware of the new directions electronics are going this century, is not a reason to attempt to drag others down to your own low level of intellect and lack knowledge in the field of modern electronics.... :-)
I think you should read some more books, unfortunately they were probably written last century, and are so far behind in the way they represent the electronics industry this century it's laughable.... Or …if you want up to date information "talk don't argue" to someone with the knowledge.
This reads like another 0zi saga :-(
FollowupID: 384282
Follow Up By: Breadman - Tuesday, Sep 13, 2005 at 12:15
Tragic some of the drivel that gets posted here
Oh dear look at the abuse you want to dish out because of your lack of knowledge. Abuse is no defence for your total lack of knowledge and misinformation. You cannot even point to this so called information
LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL oh dear how sad they try and attempt to defend their incorrect misinformation by abuse
FollowupID: 384288
Follow Up By: Mainey (WA) - Tuesday, Sep 13, 2005 at 12:53
I'm sorry Mr breadman that you feel you are being abused, I assure you that is truly not my intention here, as I'm only attempting to show you that you are presently not up to date with the NEW technology of modern electronics in the 21st centaury, and yes I have done that, haven’t I, roflmao
As to your tragic statement that "I can't even point to this so called information" No one has asked questions of this technology prior to today, as a matter of fact, not many people are aware of it, the fact is it's Australian leading edge technology and presently I'm not prepared to put a link to it till it's been authorised and registered.
As I said it's NOT called an inverter.
The childish lol's you use indicate what.. your frustration ??
FollowupID: 384297
Follow Up By: Breadman - Tuesday, Sep 13, 2005 at 13:38
LOL LOL LOL caught out for telling whopper furphys
you must hold some sort of record for posting misinformation and furphys
"Australian leading edge technology" LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL LOL another one like the magical non existent vapourware never exist portable Australian fuel cells everybody was going to have in their caravans and campervans
caught with more than your pants down little boy
FollowupID: 384302
Follow Up By: Mainey (WA) - Tuesday, Sep 13, 2005 at 13:56
Your reply above is typical of someone with nothing useful to post.
As I said you are obviously not aware of the new technological changes happening in the electronics industry in the 21st century, because if you were you would be knowledgeable in the subject.... but your not – simply because you are unaware of it.
Your only way of demeaning a post that you don’t agree with is to ‘shoot the messenger’
Simply because a post is technically beyond your own limited knowledge does not make it wrong!
But that you don’t have the technical knowledge to correct it – do you?
I encourage you to show me where I am wrong in the post!
FollowupID: 384309
Follow Up By: Breadman - Tuesday, Sep 13, 2005 at 14:16
well porkies and misinformation are much the same thing
"Then there are some who have a fridge powered by a 12v battery
but it does NOT use an inverter :-)" Now post more manure that is is some magical fuel cell. You firstly attempt to abuse people then you try and make them look like you, misinformed and stupid. You are not a messenger you are telling big porkies and furphys about not able to tell anything because you are telling porkies about some little fantasy you have made up and been caught out telling furphys and porkies. You are ducking and weaving like a guilty person that has been caught out. Stop telling porkies and giving misinformation.
FollowupID: 384315
Follow Up By: Mad Dog (Australia) - Tuesday, Sep 13, 2005 at 14:33
What fridge is that Mainey ? Do they have a website
FollowupID: 384323
Follow Up By: Mainey (WA) - Tuesday, Sep 13, 2005 at 16:56
Mad Dog, no it's presently not on a website, if it was I would have linked it up here to show the "0zi copi" just HOW the technology presently exists and stop his ridiculous LOL's from cluttering up the forum space.
I was informed only today the web site will be set up shortly, I did not ask if it was hours or days away from completion - but after his childish behaviour I will guarantee a link to the website will be on this thread (unless deleted) and it will clear up his childish lousy behaviour :-)
Once man thought the earth was flat, man once thought steam engines were a technological advanced machine, now battery powered cars are becoming common.
Electronics and technology changes, and we as people must change with this new technology just to stay in front, if you don’t you are left in the dark ages and maybe would still believe the world is flat or even worse, use an ice box instead of a fridge.
Have you ever wondered what type of electronic motors power electric cars and where the technology idea’s come from?
What other types of electric motors have received the technologically advanced enhancements from the new technology available today?
Do any of the present range of electronic cars use inverters? --> NOPE
however they do use power that is "ramped up"
yes, it may give a similar result to an inverter..... but it's NOT an inverter!!! is that a hint?
Just because the breadman does not have the present day technological electronic knowledge associated with battery powered cars etc does not mean others do not know how to make electronic cars that work.
FollowupID: 384346
Follow Up By: Jimbo - Tuesday, Sep 13, 2005 at 17:11
Mainey,
Have a look at Alans post
"A very nice fellow sent me this link; http://members.dodo.com.au/~landline/solarhours/index.html "
That's Ozi's website. He somehow got his name up here again and you can bet Breadman is Ozi.
Jim.
FollowupID: 384352
Follow Up By: Mainey (WA) - Tuesday, Sep 13, 2005 at 17:20
Jim
yes you are right ...... as usual
In my earlier post I even "planted" his name within the lol's
(QUOTE) The electronics are so technologically advanced, that breadman is obviously totally UNAWARE of what is available today, otherwise he would not make ridiculous statements that are factually incorrect (as in ..wrong)
LOL LOL Ozi LOL LOL LOL LOL LOL Ozi LOL LOL (end quote)
he gets a laugh each time, so he is must be happy...
FollowupID: 384354
Follow Up By: Mad Dog (Australia) - Tuesday, Sep 13, 2005 at 23:11
Thanks Mainey. I look forward to the link.
I don't know anything about electric car motors. The electric buggy at work uses a dc motor so no need for an inverter to produce ac power.
FollowupID: 384438
Follow Up By: Breadman - Wednesday, Sep 14, 2005 at 07:51
Caught out telling porkies and furphys again.
Hard to point to any information when there is none and you are telling porkies. your track records on telling porkies and furphys is greater than John Howard
No link will ever come forward or be posted as it is a lie.
FollowupID: 384461
Follow Up By: Mainey (WA) - Wednesday, Sep 14, 2005 at 12:47
Ozi
Ozi Ozi
Ozi Ozi Ozi
Ozi Ozi Ozi Ozi
your a really funny guy
you can't even post under your real name LOL
get a life..... :-)
you just want to read about the new technology because you want to make money from it.... as I have said when it's registered and online I will post a link to it, and your post will (maybe) be there to prove I'm not a liar and you are a only a malicious and vindictive person who only posts defamatory posts rather than answers to the questions you are asked.
FollowupID: 384513
Reply By: avro - Monday, Sep 12, 2005 at 22:34
OOOps
Thats 30 minutes of kettle not 3 hours.
Yes you can split amps, but its often difficult to split it evenly. A difference in specification on the load (the regulator) could see an uneven split. Not sure what the impact would be if both regulators were connected to the same battery bank, you would need expert opinion on that.
You have not indicated the size of your battery bank. That has a big impact too in charging rate, discharge rate, and spare capacity.
avro
AnswerID: 129782
Reply By: Breadman - Monday, Sep 12, 2005 at 22:48
If solar regulators are Morningstar you can hook up as many as you like together
To hook regulators in tandem requires them to be precision regulators. Morningstar is your only reasonably priced precision regulator
Morningstar website
In low current regulators up to 30 amp this is the top line brand used by reputable installers
Other brands are desperately trying to play catchup games to Morningstar
AnswerID: 129788
Follow Up By: Mainey (WA) - Tuesday, Sep 13, 2005 at 13:26
Ozi recommends the PowerTech range of regulators on his website...
why is he wrong ?
Breadman,
can you ‘please’ advise people reading this thread why you believe Morning Star are a superior solar regulator to Steca solar regulators.
What benefits are available from the Morning Star regs that you believe are not available from the Steca range of solar regulators?
Please,
only as a guide to the people who may be interested in the subject of solar panels and regulators watching this thread, and interested in gaining information from your knowledge on the subject.
FollowupID: 384299
Follow Up By: Breadman - Tuesday, Sep 13, 2005 at 14:18
whose Ozi?
not worth explaining to a person that cannot understand basics
FollowupID: 384316
Follow Up By: Mainey (WA) - Tuesday, Sep 13, 2005 at 17:03
very true roflmao
So I won't waste my time or yours either by attemping to explain it to you
because as you have said it's...
"not worth explaining to a person that cannot understand basics"
your words not mine :-)
FollowupID: 384349
Reply By: Alan Southport QLD - Tuesday, Sep 13, 2005 at 09:54
Ok,
Thanks everyone for your replies.
Someone mentioned about the battery capacity, it was mentioned, but here it is any way - 12 Trojan T105's 6volt each - so working as 6 12volt batterys - each 12volt battery is rated at 225aph - i think that's right.
I measured the 12vlt Amps with a DC Cable multimeter on the POS lead going FROM the Batterys INTO the 3000W Inverter, which showed abut 150Amps12v dc when i used the 2000W 240v 8amp kettle.
The Inverter showed 1600W when the fridge went into compression mode (I left the thing off for 1 hour - Don't tell the wife :) to see what it would draw.
So still wondering how to work out, assuming the batteries are fully charged at say 13.00vlts and say the fridgewent into compression mode 3 times a day for 20minutes each, then ticking over at say 500W for 6 hours - if the batteries could handle it ?? Owch my head hurts :(
I have another 4 12v T105's put to one side. Tried to cable everyting up, but the solar panels i have, just didn't seem capable to keep them all going properly - so so far the sweet spot seems to 6 12v T105's - which is why i want to get 8 more panels and then hook the fridge up. Hopefully having most of the house on Solar.
As for the Regulator, i am using a standard 20Amp at the moment.
But i was hoping to get 8 * 80watt (40amps), panels on the roof of the house, and use 2 of these regulators - if i could get away with halfing the cable into each reg.
I have a spare (thank god!), cable runing into to the house (The rest of the 12v and 240v supply is well and truely buried, concreteted and condueted in), so i was hoping to use that cable, which is capable of handling 12volts 50amps.
So i don't mind if one of the regulators decides that the batteries are topped up, and the other keeps going for bit longer - of course that would apply to 'floating' the batteries as well. But they are made by the same company and are the same model. the type on e-bay selling for about $50.
I did a previous post asking about better quality regulators and was shocked at some of the prices and the quality issues with them. I spoke to the actual manufactor (long time ago), of my 20amp reg and i have no doubt of his integrity and quality of the product. Also having one super duper reg - and it fails - then you have nothing.
So, the question was (which i think was answered), yes i can 'split' the cable and feed each half into a 20amp reg.
Once again, many thanks. So just need some help in working out the fridge issue.
Cheers.
AnswerID: 129833
Reply By: garrycol - Tuesday, Sep 13, 2005 at 10:57
09.00 to 13.00 is only 4 hours not 6 hours. I assume you meant 09.00 to 15.00
AnswerID: 129847
Reply By: Mainey (WA) - Sunday, Sep 18, 2005 at 01:37
Allan, you have posted -> So, my 50ltr fridge (which has 1Amp on the power sticker)
What brand and model fridge is it that has this 1Amp sticker on it ??
AnswerID: 130627
Reply By: Alan Southport QLD - Sunday, Sep 18, 2005 at 09:02
Hello again all,
With the time, oops! I did mean 9:00am to 3:00pm.
Mainey, my fridge is a 500ltr not 50ltr i think you mean.
But the model is a Fujitsu Er 502F - W: Input current 0.7A - and The Defreosting Current = 1.0A
So i assume the 'compression' phase is the Defrosting Current, or have i got that wrong?
Alan.
AnswerID: 130635