Comment: Using Power Leads: Facts & Regulations

While the overall message about joining leads etc... is basically correct there are some technical inaccuracies on how RCDs work.
Cable size/length/impedance/loads is related to overload protection tripping times and I think there is a little confusion in the article with difference between tripping times of an Overload Circuit Breaker (MCB) and of a Residual Current Device Circuit Breaker (RCD).
RCDs work on a balance transformer and detecting differences in flow between the active and neutral in that transformer. The impedance of the cable and/or load is not relevant. A standard house/RV based RCD will trip for a current difference > 30mA for a time > 0.4s (if that's the style you have and there are several different types).
The same is not true of MCBs which can alter tripping times due to incorrect/mismatched impedance in the cables/loads. There is a very good description here (http://kevinboone.net/cableselection_web.html) of how loads and cable characteristics affect tripping times in MCB circuits. If you join the wrong cables and/or loads together the breaker may not trip at all let alone within the required time. The danger here is more related to cable overheating and fires etc. rather than personal electric shock.
Increasingly the MCB and the RCD are combine into a single device (RCBO) but the individual tripping times are still quite separate.
Anyway the take home message is still the same: joining/extending cables or "mixing" circuits and circuit breakers is not a smart move unless you understand exactly what you are doing and even if you are qualified may still be illegal in some/all states.