I think I am sufficiently qualified and licenced to comment on the matter.
....How about you.
If you have any hard information about the facts...please share.
I have the current version of AS3000 open in front of me.
And I have the previous 2 versions available to me.
Unfortunately I do not have a current copy of AS3010, though I do have AS3001 and AS3002 .....when I recently baught new standards I stopped at $1200.
The fact remains.
Non quilified electrical workers ...do not have the understanding to put an earthing system in place.
There is more to putting an earthing system in place than driving an earth stake.
If a complete earthing system is not implimented, arbitarily connecting an earth to a generator or inverter may actually make the situation more dangerous.
The facts are...
If you are operating equipment or a caravan off a portable source of supply...that is a generator or an inverter, much of the electrical protective system most take for granted in their homes simply does not work....in particular RCD earth leakage devices.
The only time that alll those protective features we have, will work is when there is a connection to a permanent installation with a fully implimented earthing system.
It is absolutely impertive that people understand, that unless either their generator or their caravan is connected to a perment installation with a full implimeted earthing system.
They must be very carefull because most of the protective measures WILL NOT WORK.
This means being absolutely sure all electrical equipment is in perfect condition.
They do not take any risks involving cables and sharp edges or jamming in metal framed doors.
No more than one, non double insulated metal cassed appliance is used with a generator or inverter....preferably onlly double insulated appliances used........in the case of a caravan.....that is the one metal cassed appliance...and all further appliance should be double insulated.
Take absolutely no risks with water, wet or damp situations.
Further proofs from the standards.
In past editions of the standards most of this was dealt with pretty simply in a couple of pages in AS3000, Theearthing issue was deakt with in a single short clause......the whole issue has expaned and combined with a number of related issues to a whole chapter with external references.
Regarding special case installations.
clause 7.3.6
The system of protective earthing in the electrical,installation shall be in accordance with section 5 of this standard as an MEN system.
Exception: where the output of the electricity gereration system does not exceed 25KVA, the output may be arranged as a seperated supply in accordance with the requirements of clause 7.4.
Because with most portable generation equipment we are unable to guarantee they will be connected to a fully implimented MEN system according to section 5 of AS3000.
The output of generators and
inverters are " arranged as a seperated supply"
clause 7.4.5
Where a seperated circuit supplies a single item of electrical equipment any exposed conductive parts of the electrical equipment SHALL NOT BE CONNECTED TO THE EXPOSED PARTS OF ANY OTHER CIRCUIT, INCLUDING OTHER SEPERATED CIRCUITS OR EARTH.
further
clause 7.4.5
Where a seperated circuit supplies more than one item of electrical equipment, the following shall apply:
(a) Any exposed conductive parts of the seperated circuit shall be connected together by an insulated equipotal bonding conductor THAT IS NOT CONNECTED TO.
(i) EARTH
(ii)a protective conductor or exposed conductive parts of another circuit, including another seperated circuit
(iii) any extranius conductive parts.
there are parts b, c,d, e...that lay firthe requiremenst of an installation.
The standards clearly state that you SHALL NOT drive an earth stake for your portable generator or inverter...nor shall you connect them to any earth or exposed metal.
good enough
cheers