I have used many extinguishers in training and real fire situations and have rarely had a DCP extinguisher fail.
I have seen an in date and in service 9 kg extinguisher fail and use out of date extinguishers for training purposes and can't recall the last time one failed.
I have used Co2 on oil fires and they work ok but in my experience, the problem with Co2 being used outside, it's effectiveness is greatly reduced due to air movement. On small oil fires they are ok but for larger fires, there would not be enough in the extinguisher to work.
I have seen re-ignition with DCP but if the burning material has a good coating of powder then the risk of re-ignition is greatly reduced.
DCP and Co2 work on the fire in different ways.
Australian Standard 1851 - 2012 is the standard which covers the service of fire protection equipment, including extinguishers. It states that once placed in service, extinguishers shall be serviced at 6 monthly, 12 monthly and five yearly intervals.
It also sets out what items are to be checked at each service interval.
At 5 years they must be discharged and internally inspected so a 10 year warranty is all
well and good but it doesn't over ride the standard.
In my opinion, DCP is the only way to go for vehicle extinguishers as they are the most effective in most scenarios. The issue with them is that they are messy.
As for the dust, its very invasive and if you try to hose it out of an engine bay, it will get into all of the crevices and set like cement.
Don't ask me how you are supposed to get it out, my job was to put it there not remove it.