AH, the dangers of the casual passer by.
How did he tell it was wired in series. Did he open
the junction box while you weren't looking?
If he didn't open
the junction box then he must be superman with Xray vision. Did he have his red undies over his trackie Daks.
If the wires going into the regulator have around 36+ volts on them when measured without any load, then it is in series.
If the voltage at that input to the regulator is around 18 and a bit volts, then it is wired in parallel. The internal connections of
the junction box would also confirm the 18V level.
18V in parallel will give twice the amp flow into batteries and charge them quickerie, normal usage.
If wired in series, unusual but can be done, the regulator firstly has to be able to withstand 36 + V just to survive and is probably rated at 50V max on the input.
In series the panels will give lower output in amps but will still give some output at lower levels of light input.
If the spec sheet max voltage of the regulator is 25 v or 30V then it is in parallel and superman isn't so super. If it is rated much higher than 36V then SM maybe correct.
If you change it from parallel as it probably is and the reg is less rated, then goodbye regulator.
You have to do some checks to make sure.