Geoff
HAS ANYONE ELSE ENCOUNTERED THE PROBLEM WHERE THE AIRCONDITIONER SHUTS DOWN WHEN THE OUTSIDE TEMPERATURE GETS TOO HOT. ANYONE KNOW OF ANY OTHER FIXES. I HAVE AN ECB BULLBAR THAT HAS THE VENT HOLES OPENED UP. I HAVE HAD THE RADIATOR TEMP SWITCH REPLACED AND THE GAS PRESSURE REDUCED. I LIVE IN THE
PILBARA SO THE AC RUNS NEARLY ALL YEAR!!
Reply By: CLIVEB - Wednesday, Sep 25, 2002 at 00:00
Wednesday, Sep 25, 2002 at 00:00
Geoff,
My GQ diesel had an aftermarket system fitted and the air supply would suddenly warm up after many kilometres on a hot day.(usually when slowing down)
Turning off the a/c for five minutes and all would return to normal.
The problem was that the evaporator was icing up,this preventing effcient heat transfer.
The problem is easily identified,as when a/c was restarted the air was getting cooler and cooler as the ice melted. The fix was to replace the t/stat which was inserted in the evap coil, meant to stop the compressor if ice build up occured.
If your compressor is cutting out on the h/p switch (high head pressure)
It could be 1.air in system 2.blocked or inneficient condensor3.if fitted ,condenser fan faults 4.lack of sufficient air flow over condenser.
The head pressure is determined by the heat rejection of the condensor,which varies depending on ambient temperature.
The only way to determine if the correct pressures exist is by connecting a gauge set. See fridge mechanic if you cannot find fault,he can determine if head pressures are correct and system free of air.