I am building a remote distribution board in my canopy.
Q] The aluminium busbars are 5mmX20mm & are threaded to take the 6mm take-offs.Should I apply threadlock for the take-offs or not?[Bear in mind there could be lots of current involved!]
Thanks.....eng
Reply By: Member - Marquis - Wednesday, Apr 26, 2006 at 19:38
Wednesday, Apr 26, 2006 at 19:38
A flat washer, spring washer then nut is all that should be required.
Note consider the spring washer to be single use only in heavy vibration areas, and make sure you do not have disimilar metal problems (ie al bar to terminal to wire metals are not compatible).
Also make sure you have fuse(s) at the power source (ie at battery) and local fuses at the board rated according to the equipment attached.
If you use circuit breakers,
check the curves are ok for the application. You may find correctly sized fuses are a better option.