earthing on generators

Submitted: Tuesday, Nov 07, 2006 at 21:47
ThreadID: 39234 Views:11455 Replies:12 FollowUps:37
This Thread has been Archived
evening all
further to mikes post below
what do people do for earthing on all these different generators and if you dont drive a stake of some sort will any earth leakage (safety swicth )equiptment still cut out in case of electric shock or other problems ????????
i believe some genies have a proper lug to attach an earth to can anybody confirm this?

steve
Back Expand Un-Read 0 Moderator

Reply By: Gob & Denny - Tuesday, Nov 07, 2006 at 21:49

Tuesday, Nov 07, 2006 at 21:49
mikes post 39204

steve
AnswerID: 203613

Follow Up By: wazzaaaa - Tuesday, Nov 07, 2006 at 22:13

Tuesday, Nov 07, 2006 at 22:13
Steve there is an interesting post that covers this subject. It is post 38360 about mid way through
Wazzaaa
0
FollowupID: 463215

Reply By: blown4by - Tuesday, Nov 07, 2006 at 23:14

Tuesday, Nov 07, 2006 at 23:14
Yes driving an earth stake in is exactly what you have to do for proper earthing. Any half decent generator will provide a lug or similar point to attach the earth cable. You are also absolutely correct in that earth leakage RCD switches will not operate unless you have a good earth. If you have the gennie sitting on a vehicle with rubber tyres you have no earth and therefore no ELB protection. It always scares me when you go to big events where hire generators are sitting all over the place, people everywhere and no proper earthing system is in place. Just relying on it being in contact with the ground is not good enough to provide a guarantee of a satisfactory earth return circuit to make the safety devices operate should a fault occur.
AnswerID: 203629

Reply By: Muzzgit [WA] - Tuesday, Nov 07, 2006 at 23:56

Tuesday, Nov 07, 2006 at 23:56
I asked the guys at the 12 volt shop this very question last week. They said it is not necessary.
AnswerID: 203634

Follow Up By: Member -Signman - Wednesday, Nov 08, 2006 at 09:14

Wednesday, Nov 08, 2006 at 09:14
It's probably not relevant, but in NSW it is an OH&S requirement that all portable type generator are earthed with a stake.
In my business I use a gennie for installation on sites with no power- and one of the first things the inspectors look for is an earth stake...
0
FollowupID: 463257

Reply By: The Fox - Wednesday, Nov 08, 2006 at 01:05

Wednesday, Nov 08, 2006 at 01:05
You need to refer to the pamphlet or to the web for your particular earth leakage safety equipment, but....

Most newer safety swithches are called RCDs (Residual Current Devices).

They are 2 poles wide in your distribution board.

Both the active and the neutral conductors are connected throught the device. They measure the current going out through the active and compare it to the current coming back through the neutral. Any difference - most measure to an accuracy of 15ma - then they trip out. The assumption is someone or something is diverting the current flow to earth.

These do not rely on earth stake.

The protection is downstream of the device, ie there is no earth leakage protection on the lead from the genie to the van.
AnswerID: 203640

Reply By: Member No 1- Wednesday, Nov 08, 2006 at 08:37

Wednesday, Nov 08, 2006 at 08:37
on safety switches...they only protect against leakage to earth...
RCD's will not protect oneself against being caught between active and nuetral and insulated from earth...you must be earth to be protected.

get a good sparky to do your wiring
AnswerID: 203655

Follow Up By: Kiwi Kia - Wednesday, Nov 08, 2006 at 13:41

Wednesday, Nov 08, 2006 at 13:41
And when was the last time you heard of someone getting caught between the active and nuetral?

An earth is not required and is not used in most countries around the world anyway.
0
FollowupID: 463310

Follow Up By: Member No 1- Wednesday, Nov 08, 2006 at 17:18

Wednesday, Nov 08, 2006 at 17:18
a child up the road.....two large (bag) sewing needles in the power point..on carpeted floor...child okay but recieved burns to finger/s?
0
FollowupID: 463377

Follow Up By: Richard Kovac - Thursday, Nov 09, 2006 at 00:33

Thursday, Nov 09, 2006 at 00:33
Member No 1

If it does not leave you it wont kill you?

must have a exit point?

That's why HV elections take small steps?

The burns are only the energy transmitted?

I don't know

Richard
0
FollowupID: 463496

Follow Up By: Kiwi Kia - Thursday, Nov 09, 2006 at 07:14

Thursday, Nov 09, 2006 at 07:14
Fair enough #1, but you must admit it is very rare. Almost all electric shocks are to an earthed object which, if we think sideways a bit is the same as the neutral in an mem (multiple earth neutral) system.
0
FollowupID: 463509

Follow Up By: Member No 1- Thursday, Nov 09, 2006 at 07:49

Thursday, Nov 09, 2006 at 07:49
yep very rare
but i only wanted to point out that do not and will not can not protect idiots who believe that "I will be ok..there's a safety switch" ...leave 240v wiring alone unless your qualified
0
FollowupID: 463515

Reply By: L33nsta - Wednesday, Nov 08, 2006 at 09:49

Wednesday, Nov 08, 2006 at 09:49
If you are only using the generator to power your caravan then the frame of the caravan should be earthed anyway so if you were inside it and a fault occurs then you will be right.

If your using items attached to the outside of your caravan attach an earth stake to your caravan frame.
AnswerID: 203665

Follow Up By: Muzzgit [WA] - Thursday, Nov 09, 2006 at 00:05

Thursday, Nov 09, 2006 at 00:05
If a caravan is sitting on rubber tyres and the jockey wheel is rubber then you are not earthed. The stabiliser legs need to be down to earth the frame.
0
FollowupID: 463490

Reply By: bruce - Wednesday, Nov 08, 2006 at 10:22

Wednesday, Nov 08, 2006 at 10:22
As an old ex Telecom man.....if you can think you can get a good earth by just driving a stake into the ground , then you live in fairy land....there are lots of variables ....and a bad earth is probably worse than none , and in my opinion a generator does not need to be earthed anyway....cheers
AnswerID: 203668

Follow Up By: Johnny boy - Wednesday, Nov 08, 2006 at 12:23

Wednesday, Nov 08, 2006 at 12:23
Hey Bruce you said EX TELECOM MAN NOT PMG So you cant be that old? LOL!! just kidden and I know what ya mean , when chasing faults the Jumperwire wrapped around the screwdriver (or earth stakes if you had one ) would usually require a Billy full of water before a good earth was established AH THE MEMORIES!!

Regards J.B.
0
FollowupID: 463293

Follow Up By: bruce - Thursday, Nov 09, 2006 at 14:42

Thursday, Nov 09, 2006 at 14:42
Eerr , no not quite right Johnny boy..I am ex PMG as well....I started in 1960 and took the so called golden hand shake in 91 ...and yes that is definately one of the many memories I have as I was a " faultman" also...cheers
0
FollowupID: 463593

Reply By: Kiwi Kia - Wednesday, Nov 08, 2006 at 13:44

Wednesday, Nov 08, 2006 at 13:44
As an interesting side point, what is an earth for anyway? First person with the correct answer I will owe a can of VB to.
AnswerID: 203701

Follow Up By: wazzaaaa - Wednesday, Nov 08, 2006 at 13:49

Wednesday, Nov 08, 2006 at 13:49
Earth is for me to live on.
Do you want my details to send the vb?
Wazza
0
FollowupID: 463312

Follow Up By: Member - Andrew (QLD) - Wednesday, Nov 08, 2006 at 13:50

Wednesday, Nov 08, 2006 at 13:50
VB is a disincentive to answer your question!

Andrew
0
FollowupID: 463313

Follow Up By: wazzaaaa - Wednesday, Nov 08, 2006 at 13:53

Wednesday, Nov 08, 2006 at 13:53
Hey I don't care free beer always tastes better than bought beer
Wazzaaaa
0
FollowupID: 463315

Follow Up By: Member - Andrew (QLD) - Wednesday, Nov 08, 2006 at 14:00

Wednesday, Nov 08, 2006 at 14:00
I would rather pay for beer than drink VB :-)

Andrew
0
FollowupID: 463318

Follow Up By: Member - Andrew (QLD) - Wednesday, Nov 08, 2006 at 16:17

Wednesday, Nov 08, 2006 at 16:17
==what is an earth for anyway==

An "earth" cable allows all exposed conductive parts or extraneous conductive parts within a MEN system to be tied to the same or approximately the same potential,
but not intended to carry current in normal service .

Am i right ;-)

Andrew
0
FollowupID: 463350

Follow Up By: Kiwi Kia - Wednesday, Nov 08, 2006 at 16:32

Wednesday, Nov 08, 2006 at 16:32
Nice one Wazza! 9/10 for ingenuity.

Andrew, That is what it does but not what it is for.
Clue; think along the safety angle and how it does it.
0
FollowupID: 463351

Follow Up By: Member - Andrew (QLD) - Wednesday, Nov 08, 2006 at 17:31

Wednesday, Nov 08, 2006 at 17:31
I hope you will be quoting the official reason here with reference........

Andrew
0
FollowupID: 463383

Follow Up By: Kiwi Kia - Wednesday, Nov 08, 2006 at 21:47

Wednesday, Nov 08, 2006 at 21:47
Wazaaaa, Andrew and anyone else that may be interested the answer is that in case of a short to earth then the fuse / rcd / mcb whatever will be tripped, blown etc. to isolate the circuit. In otherwords - turn off the power supply. The earth wire only needs to carry the fault current for enough time to trip the safety device.

Andrew, no reference required, you can put it down to what those people who set the exams call "general trade knowledge".
0
FollowupID: 463448

Reply By: Member - Norm C (QLD) - Wednesday, Nov 08, 2006 at 14:15

Wednesday, Nov 08, 2006 at 14:15
This is from a Workcover NSW document titled ' Electrical Practices for Construction Work - Draft Code of Practice' para 6.4

'Earthing of the generator frame is not required or recommended. No earth electrode is required.'

I'll leave it to others more informed on these matters to intrepret what this means.

www.workcover.nsw.gov.au/NR/rdonlyres/C71A75CF-3288-4624-A8EC-3A7A342C2BB2/0/electrical_draftcop_4494.pdf
AnswerID: 203705

Follow Up By: Member - Norm C (QLD) - Wednesday, Nov 08, 2006 at 14:40

Wednesday, Nov 08, 2006 at 14:40
My Kipor operating manual says the generator should be grounded. It says to connect heavy wire from the earth terminal to an external earth source. The accompanying diagram (if taken as being to scale) indicate an earth spike a couple of inches long. Mmmmmmmmm.
0
FollowupID: 463327

Follow Up By: Member - Andrew (QLD) - Wednesday, Nov 08, 2006 at 16:06

Wednesday, Nov 08, 2006 at 16:06
Most information covered by the various States Cope of Practices etc are generally taken from the following Standards:

- AS/NZS 3000:2000 – Australian/New Zealand Standard Wiring Rules
- AS/NZS 3010:2005 – Electrical installations—Generating Sets

Whilst Norm is correct with the Workcover statement shown, there may be exceptions:

===================================================
2.5.6.3.1 Connection of generating set bonding system. Where a generating set supplies an electrical installation that incorporates an earthing system, the bonding system of the generating set (see Clause 2.5.6.1) shall be earthed by connection to the earthing system of the electrical installation.

Connection to earth shall not be made by means of a separate earth electrode.
===================================================

Andrew
0
FollowupID: 463347

Follow Up By: Gob & Denny - Wednesday, Nov 08, 2006 at 17:26

Wednesday, Nov 08, 2006 at 17:26
goodday andrew
your as 3000 is correct for buildings etc but caravanss tents and such dont have an existing earth system to bond to
steve
0
FollowupID: 463380

Follow Up By: L33nsta - Wednesday, Nov 08, 2006 at 17:43

Wednesday, Nov 08, 2006 at 17:43
Your caravan will be earthed when you plug your extension lead into it from your generator
0
FollowupID: 463389

Follow Up By: Member - Andrew (QLD) - Wednesday, Nov 08, 2006 at 17:48

Wednesday, Nov 08, 2006 at 17:48
Thanks Gob & Denny, i believe we aren't talking about caravans etc in this sub-thread, rather gensets and earthing in general :-)

You are indeed correct, hence their requirements to conform to AS/NZS 3001:2001 :
Electrical installations - Relocatable premises (including caravans and tents) and their site installations, and not AS3000 ;-)

Andrew
0
FollowupID: 463390

Follow Up By: Gob & Denny - Wednesday, Nov 08, 2006 at 18:30

Wednesday, Nov 08, 2006 at 18:30
l33
to what or where will it be earthed ?
a generator sitting on 4 rubber feet will not conduct an earth nor will a caaravan sitting on 4 rubber tyres and a rubber jockey wheel

steve
0
FollowupID: 463402

Follow Up By: L33nsta - Wednesday, Nov 08, 2006 at 18:47

Wednesday, Nov 08, 2006 at 18:47
Gob & Denny in your last post you are correct in stating that power can't go through normal rubber. (please don't test this theory)

The extension lead going from your generator to your caravan. It has 3 pins; active, neutral and earth.

So those 3 wires are going into the caravan. On your caravan inlet plug or at the caravan switch board there will be a wire going from the earth pin to the chassis of the caravan. This is how you get your earth in the caravan.

I hope this explains it a little better.

Sorry to take this thread a little off topic.
0
FollowupID: 463406

Follow Up By: Kiwi Kia - Wednesday, Nov 08, 2006 at 21:36

Wednesday, Nov 08, 2006 at 21:36
Hi L33nsta, This would actually be an equal potential bonding link and not a true earth as it is not conected to the general mass of the earth.
0
FollowupID: 463438

Follow Up By: techo2oz - Thursday, Nov 09, 2006 at 06:29

Thursday, Nov 09, 2006 at 06:29
Ah! But if you had a good quality heavy duty extension lead, plugged into the Genset ,and as per the instruction manual, driven your "couple of inch long" earth stake into the dry dusty ground.... And this stake was then bonded to the earth lug supplied.

You would have that nice warm fuzzy feeling that all is well with the world and you and yours are safe.

While I am not old enough to know the PMG days personally, I personally know a few young PMG people. And the tales they tell of earthing...

Cheers
0
FollowupID: 463507

Reply By: Geoff (Newcastle, NSW) - Wednesday, Nov 08, 2006 at 19:33

Wednesday, Nov 08, 2006 at 19:33
Hi Steve,
You've raised an extremely important subject here and one that has many experienced electrical engineers devote the whole of their careers to its study, earthing. More importantly, safe and functional earthing.

If you go to your local mine site with a generator they'll mostly require you drive an earth stake and then perform some form of earth bond resistance check. Basically a check to see how well the earth stake is connected to the surrounding ground. They also require the use of Residual Current type Earth Leakage Circuit Breakers.

As others have stated above, Workcover (NSW) doesn't require a generator to have an earth stake but does require an Earth Leakage Circuit Breaker of the Residual Current type. The operation of these has been described above.

As Nudie has quite correctly pointed out an Earth Leakage Circuit Breaker (ELCB) will not protect you from connecting yourself between Active and Neutral. Mind you, no Circuit Breaker will protect someone's life from this type of accident. They will probably protect you from becoming black and crisp. As to the comment regarding the the commonality of this type of accident, the bulk of modern deaths (post compulsory ELCB) from electrical shock are Active to Neutral human connection.

Now, onto your question regarding earthing, generators, camping and your caravan. This is a wholely interesting and little understood subject by almost all users and most electricians! My theory on this is they don't actually draw the circuit then analyse the potential points of failure before happily wiring.

You've raised a valid point regarding the earthing of your caravan, yes it does sit on at least two rubber tyres and a rubber jockey wheel so it isn't actually connected directly to the planet earth. What happens with your caravan is every part of the metal frame, skin and chassis are required to be bonded to the earth conductor of your 240 Volt supply. That bonding point is also required to be accessible for inspection and maintenance.

My take on portable equipment and earthing is this, you absolutely must have a Residual Current type Earth Leakage Circuit Breaker as close as possible to the generator outlet. Everything you run off the generator MUST be downstream of this device.
For me, when running a generator that is NOT subject to a Mines or Workcover ruling, (Both these requirements overrule anything I say or use) I bond the earth to the neutral, UPSTREAM of the Residual Current device.
Why? I'm creating an Multiple Earthing Neutral (MEN) Link just like your house has. What advantage does it offer? There is no path to earth downstream of the ELCB that the ELCB cannot detect. The system is reasonably fail safe.

Note: I did say a couple of paragraphs above to DRAW the circuit and potential fault circuits. Then thoroughly analyse the potential paths for current flow. Don't forget when using portable generating plant it's possible to connect yourself between Neutral and Earth and die. Less than 20mA will stop your heart.

Disclaimer: I offer the above as opinion only. It DOES NOT constitute advice or recommendation of portable generating plant connectivity or offer absolute safety from electric shock whilst operating portable electrical generating and consuming equipment. Hell the generating professionals even blew up a main station transformer in NSW today!!

Geoff.
Geoff,
Landcruiser HDJ78,
Grey hair is hereditary, you get it from children. Baldness is caused by watching the Wallabies.

Lifetime Member
My Profile  My Blog  Send Message

AnswerID: 203770

Follow Up By: L33nsta - Wednesday, Nov 08, 2006 at 21:59

Wednesday, Nov 08, 2006 at 21:59
Geoff is this statement correct and if so can you please explain?

Geoff Wrote:
Don't forget when using portable generating plant it's possible to connect yourself between Neutral and Earth and die.
0
FollowupID: 463456

Follow Up By: Geoff (Newcastle, NSW) - Wednesday, Nov 08, 2006 at 23:17

Wednesday, Nov 08, 2006 at 23:17
Hi L33nsta,
Naah, not the slightest bit correct made that up just to see if you're awake.

Mate, read the whole paragraph, especially the bit about DRAWING what you have. Generator outputs float above earth, neither side is actually tied to earth. Unlike the MEN system in a house.
Therefore the Active and Neutral of a generator supply are each at the same potential above earth meaning each has the same ability to pass current to earth.

My original paragraph,
"Note: I did say a couple of paragraphs above to DRAW the circuit and potential fault circuits. Then thoroughly analyse the potential paths for current flow. Don't forget when using portable generating plant it's possible to connect yourself between Neutral and Earth and die. Less than 20mA will stop your heart."

Hope that makes sense,

Geoff.
Geoff,
Landcruiser HDJ78,
Grey hair is hereditary, you get it from children. Baldness is caused by watching the Wallabies.

Lifetime Member
My Profile  My Blog  Send Message

0
FollowupID: 463480

Follow Up By: Kiwi Kia - Thursday, Nov 09, 2006 at 07:21

Thursday, Nov 09, 2006 at 07:21
Hi Geoff, Am I missing something?

First you say that the generator outputs float above earth then you say that the active and neutral of a generator are each at the same potential above earth meaning each has the same ability to pass current to earth.

If they are above earth and floating and you do not have a generator conection to earth how do they have the ability to pass current to earth?
0
FollowupID: 463511

Follow Up By: hl - Thursday, Nov 09, 2006 at 07:40

Thursday, Nov 09, 2006 at 07:40
Hi....
Precisely.... if the generator is NOT earthed, you can happily hold the active or the neutral in your hand (but not that the same time!) and nothing will happen to you. If you don't use an RCD, then there is little point in earthing it, in my opinion. In fact, it will probably be more dangerous if it IS earthed in that situation.

Cheers

0
FollowupID: 463513

Follow Up By: Geoff (Newcastle, NSW) - Thursday, Nov 09, 2006 at 08:38

Thursday, Nov 09, 2006 at 08:38
Hi Kiwi,
What I am saying is that any conductor that has a potential difference to earth has the potential to pass that current to earth if given a path.
What I'm also saying is don't just blindly assume everything is perfect in the world of generators and power. If the potential for an accident exists at some point in time that accident will happen.
We use these systems in an imperfect environment, sometimes damp usually around children and they aren't usually maintained well.
So understand what you have, understand its dangers and treat the risks accordingly.

Geoff.
Geoff,
Landcruiser HDJ78,
Grey hair is hereditary, you get it from children. Baldness is caused by watching the Wallabies.

Lifetime Member
My Profile  My Blog  Send Message

0
FollowupID: 463525

Reply By: shaggy - Tuesday, Nov 14, 2006 at 10:53

Tuesday, Nov 14, 2006 at 10:53
Hi all,
in the military, they earth all generators, and the rules say that the soldiers are supposed to pee on the earth stake to ensure a nice saline moist earth with good conductivity.
Cheers
AnswerID: 204851

Reply By: gottabjoaken - Tuesday, Nov 14, 2006 at 13:32

Tuesday, Nov 14, 2006 at 13:32
Well, here is a question... But then since I know as little as most, the answer may already have been provided above - I just don't understand it

What is the earth pin on the generator outlet connected to, behind it?

The frame of the generator?

What is the use of that?

Is there a any device that will trip when the earth leaking current has nowhere to go, and so therefore will peak (to a low limit) for an infinitesmal time and then be zero?

Surely the purpose of grounding the earth is so that there is something to absorb current for long enough so that the safety devices can detect it?

I hear you about RCD rather than ELCD. Is that all there is to it? A difference in current between active line and neutral line means it is going somewhere else?

So I would expect that a caravan frame/shell could easily be live without any warning, because there is no current going anywhere, until you touch it while you have bare feet on wet ground.

Ken

AnswerID: 204879

Follow Up By: Mike Harding - Tuesday, Nov 14, 2006 at 14:06

Tuesday, Nov 14, 2006 at 14:06
>What is the earth pin on the generator outlet connected to, behind it?

>The frame of the generator?

Yes.

>What is the use of that?

None, really - unless you have the gen earthed then it makes sense

>Is there a any device that will trip when the earth leaking current
>has nowhere to go

If it has nowhere to go... it won't go anywhere... so will not be detected by an ELCB/RCD device.

>Surely the purpose of grounding the earth is so that there is
>something to absorb current for long enough so that the safety
>devices can detect it?

Yes - as Kiwi Kia pointed out above.

>So I would expect that a caravan frame/shell could easily be live
>without any warning, because there is no current going anywhere,
>until you touch it while you have bare feet on wet ground.

Providing the gen is _not_ earthed you could touch a "live" caravan which doing the Highland Fling in a steel bath full with salt water. In this condition the gen, and van, are a floating system and in order for current to flow you would have to touch the gen neutral. I am assuming earth and neutral are not bonded at the van distribution board.

Mike Harding
0
FollowupID: 464776

Follow Up By: gottabjoaken - Tuesday, Nov 14, 2006 at 14:19

Tuesday, Nov 14, 2006 at 14:19
Well, Mike,

No, but the concern is when something goes wrong and a conductor comes into contact with the frame/skin of the caravan, or an applialce fails to its frame and therefore the circuit earth.

Then, Yes, the active or the neutral IS in contact with the van metallic parts, and so when you walk up to it and touch it, then you provide the path to earth.

A floating system is fine while you are IN the system, but surely, the problem arises when you provide the breach to another system - earth or any different potential.

So why is it not MANDATORY to have an earth on the generator, and what is more important, a BETTER earth than you can provide with your wet hands and wet feet...

Ken
0
FollowupID: 464783

Follow Up By: Mike Harding - Tuesday, Nov 14, 2006 at 14:29

Tuesday, Nov 14, 2006 at 14:29
Ken:
If the generator is not connected to earth then the _only_ (repeat only) path for current to flow from that gen is from it's Active pole back to it's Neutral pole. The earth is not a factor in this equation (ignoring the gen frame).

So if something in the caravan develops a fault such that the active pole of the gen becomes connected directly to the metal frame of the caravan and you touch the caravan frame while standing in bare feet on wet grass you will not receive a shock, _providing_ the gen is not earthed. The reason is that the gen has no reference to earth - it knows nothing about it and current cannot return to the gen's neutral pole via earth unlike in the domestic system where, essentially, earth and neutral are, electrically, the same. In order to get a shock your body would have to complete a circuit between the gen's active and neutral and it cannot do that via earth with a gen which is not earthed. Is that any clearer? :)

Mike Harding

mike_harding@fastmail.fm
0
FollowupID: 464785

Follow Up By: gottabjoaken - Tuesday, Nov 14, 2006 at 14:40

Tuesday, Nov 14, 2006 at 14:40
Well, thanks for that, Mike.

Not that I don't believe you, but I am sure that you wouldn't be offended when I say I would rather take your statement on faith, rather than try to prove you right. (LOL).

I always envisaged the "earth" to be just something that would absorb the current (negate the electrons) without having to provide a circuit back to the power source.

Glad to hear that is not so.

In a past life (not literally !) I have demonstrated field telephones working perfectly with a single conductor and earth return, and there is no way I can believe the return current actually passed through 20 kilometres of dirt. And that was only a low voltage.

Ken
0
FollowupID: 464789

Follow Up By: Mike Harding - Tuesday, Nov 14, 2006 at 14:49

Tuesday, Nov 14, 2006 at 14:49
Hi Ken

Earth can vary between being an excellent conductor and a very poor (useless) one depending upon the soil/rock types, wetness, salt levels etc.

A number of places in Oz (Dargo in the Vic High Country springs to mind) use a single wire supply for their domestic mains and rely totally on the earth as a return. I suspect in certain conditions Dargo will see voltages well below 240V :)

Because the field telephone uses a low current it can tolerate quite high resistance in the paths between handsets, even so 20km is a respectable distance - bet you would struggle to get that in the deserts though? :)

Mike Harding
0
FollowupID: 464791