Using a generator to charge batteries

Submitted: Tuesday, Feb 13, 2007 at 21:53
ThreadID: 42280 Views:10498 Replies:11 FollowUps:27
This Thread has been Archived
Question about sizing a Battery Charger to Generator capacity.

I searched the Archives for a while but got lost in the absolute maze and plethora of posts on this topic without actually answering my question. I did however find LOADS of opinions on Honda v Yamaha!

I have a Honda 1KVa generator and am in the market for an appropriately sized 240v charger to recharge a battery bank of 2 x 100AH SLA batteries located in the Camper.

Can you electro gurus tell me the best sized charger in terms of 12v Charging Amps that the generator will support within a continuous load rating of 900 watts while not providing TOO many Amps that the batteries will not take the charge?

On a previous trip I have had a 6 Amp and a 15 Amp charger both running off the generator doing some recharging and the genny did not raise a single RPM from the Eco-Throttle setting.

The Genny has a DC charging outlet capable of providing 8 Amps which I saw somewhere equates to 100 Watts of 240v load which is barely raising a sweat for a genny capable of 900W continuous load. Does this mean that I could run a 240v 50 Amp charger with Watts to spare?

The aim is to be able to pump max Amps back into the batteries to minimise generator run-time without exceeding the capacity of the batteries to accept the charge quickly enough.

Your thoughts appreciated.

Muddy

Back Expand Un-Read 0 Moderator

Reply By: Bonz (Vic) - Tuesday, Feb 13, 2007 at 22:01

Tuesday, Feb 13, 2007 at 22:01
Muddy Muddy Muddy, you have to have apples and apples mate, a 240v 50 amp charger is 50 amps at 12v mate = 600w give or take a few friendly watts, so yes you could run it easily off the genny. Now not sure watt the batteries will accept 50 a is big charging current and you may boil them, I dunno about that, but as for the genny it will eat it with lots of Watts to spare
.
Time is an illusion produced by the passage of history
.

Lifetime Member
My Profile  My Blog  My Position  Send Message
Moderator

AnswerID: 221537

Follow Up By: Redback - Wednesday, Feb 14, 2007 at 09:54

Wednesday, Feb 14, 2007 at 09:54
My understanding with deep cycle batteries is that they will last longer and preform better charging them slowly.

Fast charging is not good for any battery.

Baz.
0
FollowupID: 482333

Follow Up By: Member - Jeff M (WA) - Thursday, Feb 15, 2007 at 12:00

Thursday, Feb 15, 2007 at 12:00
Spot on Bonz, but in saying that fast charging IS good for getting the beer cold if the fridge has stopped! LOL

If you have a good 3 stage charger it should not matter AS much because it will only charge them on bulk for a short period. If you were using a truck charger type thing that was just blatting them full on it would not be good. But being Gel Cell battereis you would need a 3 stage that supported that type of battery anyway. You'll find that they need to bulk charge at about 14v, then switch to about 14.7v then float at 13.8v or so. If the charger supports these batteries it will either have a switch to set it to Gell Cell type batteries or the really expensive smart ass ones may even do it automatically, but I would suggest finding one with a switch.
0
FollowupID: 482618

Reply By: SA_Patrol - Tuesday, Feb 13, 2007 at 22:15

Tuesday, Feb 13, 2007 at 22:15
Have you every seen the Honda Outback Battery Chargers. It might be the best thing to use for what your doing.

www.christieengineering.com.au/
AnswerID: 221542

Follow Up By: Member - Roachie (SA) - Tuesday, Feb 13, 2007 at 22:27

Tuesday, Feb 13, 2007 at 22:27
I'm guessing he probably doesn't want to carry another petrol motor'd contraption around with him. The Christie is a good thing for what it was designed to do, IMHO. However, it is significantly noisier than the gennie and it only has one purpose. The gennie is not only much quieter, but has the added benefit of being able to run 240v appliances.......INCLUDING a battery charger.

In short, the gennie can cover all the bases that the Christie can do; but not vice versa.
0
FollowupID: 482276

Follow Up By: Muddy doe (SA) - Tuesday, Feb 13, 2007 at 22:34

Tuesday, Feb 13, 2007 at 22:34
Yeah - what HE said!

Thanks very much for the idea though....

Cheers
Muddy
0
FollowupID: 482278

Reply By: Member - Roachie (SA) - Tuesday, Feb 13, 2007 at 22:30

Tuesday, Feb 13, 2007 at 22:30
Muddy,
That 15amp unit of mine does the job on my 2 x 100ah in the camper trailer lickety split mate, a 25amp unit would be that much better and your 2 batteries would love you forever (or at least until they kark it....hahahaha)
AnswerID: 221546

Follow Up By: GaryInOz (Vic) - Wednesday, Feb 14, 2007 at 10:38

Wednesday, Feb 14, 2007 at 10:38
Even at 25 amps it would still take about 10 hrs or so to fully chage both batteries (including "charging losses"). Depending on the type of battery you may well be able to go higher than this.

Remember also that there may be some switchmode chargers (usually identified by the abscence of a large heavy transformer inside) that may not run with some of the raw AC generated by some generators ("dirty AC").
0
FollowupID: 482339

Follow Up By: disco1942 - Wednesday, Feb 14, 2007 at 12:34

Wednesday, Feb 14, 2007 at 12:34
The way to fix that problem is to also run a 75 or 100 W incandescent light whilst running the charger. This puts a load onto the generator that settles it down.

PeterD
PeterD
Retired radio and electronics technician

Lifetime Member
My Profile  Send Message

0
FollowupID: 482365

Reply By: Geoff (Newcastle, NSW) - Tuesday, Feb 13, 2007 at 22:54

Tuesday, Feb 13, 2007 at 22:54
"Does this mean that I could run a 240v 50 Amp charger with Watts to spare?"

That about sums it up,
I've got the use of a 30 Amp charger connected to the 240 Volt outlet on my EU10i Honda, the gennie doesn't even raise a sweat.

For general information the following picture is an oscilloscope capture of the 12V DC from my Honda. Funny thing, it's actually 25V DC and nothing like DC. There's no way I'd use the DC output of any generator for battery charging.



I've done the same test on a few different brands of generator DC outputs and they aren't all that useful for charging batteries. For practical purposes they are all the same.

So, your plan to use a 50Amp charger is a great idea.

Geoff
Geoff,

Grey hair is hereditary, you get it from children. Baldness is caused by watching the Wallabies.

Lifetime Member
My Profile  My Blog  Send Message

AnswerID: 221555

Follow Up By: Muddy doe (SA) - Tuesday, Feb 13, 2007 at 23:14

Tuesday, Feb 13, 2007 at 23:14
Yeeeesss....

The output from the DC connection would not seem to be a lot of good for the batteries based on that reading! And 8 Amps charging current is going to be a slow way of doing the job!

Looks like I am going to be looking at a 25 Amp 240v Smart Charger which will give the batteries a good drink while also leaving capacity to run the fridges (70 litre Trailblazer and sometimes a 40 Weaco) and computer direct off 240 while the genny is running and give the batteries a good rest.

As Bonz pointed out above a 50 Amp charger is pretty huge and probably pretty big dollars as well as physical size. Suffice to say that genny capacity is not a problem for running a battery charger and that is what I wanted to know.

Wonder if people out there realise how little of their genny capacity they are using if they only use a 1 or 2 KVa genny for charging batteries....

Cheers
Muddy
0
FollowupID: 482292

Follow Up By: Geoff (Newcastle, NSW) - Tuesday, Feb 13, 2007 at 23:26

Tuesday, Feb 13, 2007 at 23:26
"The output from the DC connection would not seem to be a lot of good for the batteries based on that reading! And 8 Amps charging current is going to be a slow way of doing the job!

Looks like I am going to be looking at a 25 Amp 240v Smart Charger which will give the batteries a good drink while also leaving capacity to run the fridges (70 litre Trailblazer and sometimes a 40 Weaco) and computer direct off 240 while the genny is running and give the batteries a good rest."

You've summed it up perfectly,

Geoff
Geoff,

Grey hair is hereditary, you get it from children. Baldness is caused by watching the Wallabies.

Lifetime Member
My Profile  My Blog  Send Message

0
FollowupID: 482294

Follow Up By: GaryInOz (Vic) - Wednesday, Feb 14, 2007 at 10:46

Wednesday, Feb 14, 2007 at 10:46
Did you actually have a load connected when you took that screen cap??? Have you ever wondered why they recommend that you do not disconnect the battery of your car when the engine is running????? This is EXACTLY why.

The charging output (of the gennie, and the cars alternator) needs a battery connected to to regulate the output.

Deep and meaningful discussions could ensue from here on, but sufficient to say being armed with half the information is not necessarily helpful...

Hook a battery up to the charger output on the gennie and then show us the waveforms as well as the measured voltage and measured current.
0
FollowupID: 482342

Follow Up By: disco1942 - Wednesday, Feb 14, 2007 at 13:23

Wednesday, Feb 14, 2007 at 13:23
When you apply a significant load to the DC output on a portable generator it will drop down to 13 V or less. This makes it not very good for battery charging purposes. It is useful however to put enough charge back into a battery to start an engine.

PeterD
PeterD
Retired radio and electronics technician

Lifetime Member
My Profile  Send Message

0
FollowupID: 482382

Follow Up By: Geoff (Newcastle, NSW) - Wednesday, Feb 14, 2007 at 22:10

Wednesday, Feb 14, 2007 at 22:10
No sheite Sherlocks?

Geoff
Geoff,

Grey hair is hereditary, you get it from children. Baldness is caused by watching the Wallabies.

Lifetime Member
My Profile  My Blog  Send Message

0
FollowupID: 482518

Reply By: drivesafe - Tuesday, Feb 13, 2007 at 23:34

Tuesday, Feb 13, 2007 at 23:34
Hi Muddy doe, unlike most electrical things around your vehicle, which are marked 12 volts and thats what you use to calculate the power usage, when working out the power usage of a battery charger you have to base your calculation on the maximum current output x the charging voltage.

So if your charger is capable of producing 50 amps while charging at 14.5 volts, then you will need 725 watts to cover the out put of the battery charger and probably about an additional 10% to cover the inefficiencies of the battery charger itself, so you will need about 800 watts.

Now this is only when the charger is running at full power.
AnswerID: 221565

Reply By: Derek from Affordable Batteries & Radiators - Tuesday, Feb 13, 2007 at 23:37

Tuesday, Feb 13, 2007 at 23:37
Hi Muddy

Our 25 amp Smart Charger is suited to 1ka but remember the smaller Honda is prone to glaze the bore at idle or on eco so best to put a slight load on while charging the batteries. A 100w lamp should do the trick.

Regards

Derek.
AnswerID: 221566

Follow Up By: Geoff (Newcastle, NSW) - Tuesday, Feb 13, 2007 at 23:49

Tuesday, Feb 13, 2007 at 23:49
Or,

"leaving capacity to run the fridges (70 litre Trailblazer and sometimes a 40 Weaco) and computer direct off 240 while the genny is running and give the batteries a good rest"

Would form a handy base load along with the charger,

Geoff
Geoff,

Grey hair is hereditary, you get it from children. Baldness is caused by watching the Wallabies.

Lifetime Member
My Profile  My Blog  Send Message

0
FollowupID: 482298

Follow Up By: Derek from Affordable Batteries & Radiators - Tuesday, Feb 13, 2007 at 23:52

Tuesday, Feb 13, 2007 at 23:52
Hi Geoff

Yes, quite right.

I also use the time to charge the laptop and boil the jug on my EU2.0

0
FollowupID: 482299

Reply By: Mainey (WA) - Wednesday, Feb 14, 2007 at 01:42

Wednesday, Feb 14, 2007 at 01:42
Think first and foremost about the two batteries........ use a 20 Amp, 240v charger.

Work on about 10% of max battery capacity to recharge it/them.
Two or three stage chargers are dearer but far more effective.

Your vehicle alternator may be 60 to 110 amps, however those amps are first run through a "regulator" before getting to the battery, so the battery does not get 'destroyed' and it will only deliver about 2 amps when the battery is close to 'full' and when 'full' it delivers effectively nil.

However a decent Solar system is "in my own opinion" unbeatable and also cheaper than a Honda, as the batteries do not get to run down below 12.6v because the Solar system is replacing the power as it is being used during the day, and fully recharging the battery as soon as the fridge stops running, so at nightfall the battery is still 'fully charged' and if it's a decent sized AGM it will still be showing above 12.6v early next morning - and all without you lifting a finger. lol
AnswerID: 221581

Follow Up By: GaryInOz (Vic) - Wednesday, Feb 14, 2007 at 10:56

Wednesday, Feb 14, 2007 at 10:56
An internally regulated alternator can give up to (your) "60 to 110 amps" at the terminal on the alternator, it cannot "push' current out if there is nothing to absorb it

The "regulator does nothing to regulate any current output, it regulates the output VOLTAGE of the alternator only. The amount of current charge the alternator puts out is a respose to the difference between the battery voltage and the voltage that the alternator has been set to. As the battery voltage rises (from being charged) "to meet" the alternator set voltage, the current reduces (ohms law, NOTHING to do with the regualtor).
0
FollowupID: 482344

Follow Up By: Mainey (WA) - Wednesday, Feb 14, 2007 at 11:35

Wednesday, Feb 14, 2007 at 11:35
Gary,
I can only assume the two batteries are connected to the alternator/regulator, lol
0
FollowupID: 482353

Follow Up By: disco1942 - Wednesday, Feb 14, 2007 at 13:19

Wednesday, Feb 14, 2007 at 13:19
Also remember a vehicle alternator puts out 13.5 - 14 V when the motor warms up due to the temperature compensation built into the alternator. This is less than the output of a three stage charger in the absorption stage - so a battery will not receive full charge if you use a vehicle alternator to charge it.

PeterD
PeterD
Retired radio and electronics technician

Lifetime Member
My Profile  Send Message

0
FollowupID: 482381

Follow Up By: Mainey (WA) - Wednesday, Feb 14, 2007 at 14:38

Wednesday, Feb 14, 2007 at 14:38
Peter,
Simplistically stated, while the alternator/regulator is putting out more power than what is in the battery, the battery will be relieving a charge.

Eg, if the Alternator/regulator is putting out 13.5v and the battery is only 12.2v the battery will become fully charged at 12.66v (wet cell Cranking battery) because the power going into the battery is greater than the power contained with-in the battery, said with-out using any 'big words' lol.
The battery will show as 13.5v when tested, while being actually charged, however this is known as surface charge and will disapate when the charging stops.

Some explain it using the 2 x buckets of water syndrome, if bucket (a) is 50% full and bucket (b) is 100% full, and a tube is run from the base of (a) to the base of (b) the water will level out in both buckets at 75% full, however if you continue to add water to bucket (a) it will continue to add water via the tube to bucket (b) till (a) is also full.
0
FollowupID: 482396

Follow Up By: disco1942 - Wednesday, Feb 14, 2007 at 15:19

Wednesday, Feb 14, 2007 at 15:19
Mainey

We can not use simplistically stated statements when calculating charge currents into batteries. The old bucket of water is only good for explaining purely resistive circuits. When you start talking about capacitive, inductive or chemical loads things get complicated and other things have to be taken into account.

There is a magic figure of 2.2 V/cell which is the voltage above which has to be exceeded to put any charge into a well charged battery. Sure a discharged battery will take some current from a lesser voltage but not much current. I once had a small, fairly well discharged car battery that I used a regulated power supply to charge - I had to wind up the voltage to its maximum (16.5 V) to get 1.5 A into the battery - it took nearly an hour before the current came close to the PSUs maximum of 10A and I had to commence reducing the voltage to prevent the overload circuit cutting the output off. This should demonstrate to you that it is not a simple bucket of water or Ohms Law situation when you start to calculate battery dynamics so you can forget your buckets of water.

Manufacturers of three stage battery chargers do not set their absorption voltage at 14.4 to 14.7 V for no valid reason when they recommend their chargers for charging batteries with a 20 hour capacity of up to 25 times their maximum output current. This voltage incidentally is a lot higher than a car's alternator runs at when the engine bay is at running temperature.

PeterD
PeterD
Retired radio and electronics technician

Lifetime Member
My Profile  Send Message

0
FollowupID: 482402

Follow Up By: drivesafe - Wednesday, Feb 14, 2007 at 20:09

Wednesday, Feb 14, 2007 at 20:09
Actually, you are both off the mark.

Automotive type batteries, whether they be wet cell, Gel Cell or AGM, will not fully charge unless the charging voltage is 13.8 or higher ( this will vary slightly between makes ) and as most alternators have a constant output voltage of between 14 to 14.3 volts, there is no reason why your alternator can not charge all your automotive batteries to at least 95%, given enough time.

With exception of the Discovery 3 and Range Rover Sports, if your alternator is running at less than 14 volts once the motor is at it’s normal operating temperature, it’s time to have your regulator checked.

All batteries require at least 13.8 volts at 25c to get the chemical reaction working properly to allow the battery to take a full charge.

Anything above this 13.8 mark will simply speed up the charging rate. In other words, the high the voltage over 13.8 volts, the quicker your batteries will charge.

Note, there is an upper limit to how high a voltage a given battery can take without damaging it. This upper limit varies greatly between makes and types of batteries.

Always go to the web site of the manufacturer of what ever brand battery you are using and get the correct charging info for your specific battery.

Cheers
0
FollowupID: 482477

Follow Up By: disco1942 - Wednesday, Feb 14, 2007 at 23:46

Wednesday, Feb 14, 2007 at 23:46
drivesafe

Auto alternators have temperature compensation. For an example of their curves see www.landiss.com/battery.htm - The voltages you are quoting are for engines that have their bonnets up and their engine compartments are not up to running temperature or they have been sitting for a while and have cooled down before restarting and the alternator voltage tested. Both my disco TDi and Td5 output 14.4 V when first started and drop to 13.7 V about 5-10 km down the road. This is sufficient for the starting battery to recover.

The general consensus among electrical engineers is that 13.8 volts is only a maintenance type charge, it takes a higher voltage to achieve a top up type charge.

For a fuller understanding on the subject of deep cycle house type batteries have a look at
http://www.victronenergy.com/upload/documents/Book-EN-EnergyUnlimited.pdf
Take particular note of sections 5.2.2 and 5.2.3.1 Automotive electricians have a simplified view of battery charging as they are only schooled to any depth in starting type batteries. To get a good understanding of deep cycle batteries you need to consult a marine electrician who has had extensive experience with boats that people live aboard.

PeterD
PeterD
Retired radio and electronics technician

Lifetime Member
My Profile  Send Message

0
FollowupID: 482545

Follow Up By: drivesafe - Thursday, Feb 15, 2007 at 00:11

Thursday, Feb 15, 2007 at 00:11
Nothing beats hands on experience, so my recommendation is that anybody wishing to find out just how there alternator is charging, is to measure the voltage at the battery after you have had a bit of a drive.

My D1 was always 41.1 volts no matter what the temperature was.

Never bothered measuring my D2 ( didn’t have it long enough ).

My Mk III RR is rock solid 14.3 at all times, hot cold or otherwise.

My D3 varies and as stated, like the RRS, is the exception to the norm.

Some late model D2s do have a varying voltage but this is because they were the first stages of the new system found in D3s and RRSs.

Of the many vehicles I have installed dual battery systems in, few had a continuous voltage level of less that 14 volts.

Don’t care what one reads in a text book or similar, I design and manufacture dual battery controller and base their development on out-in-the-field findings.

There are a very small number of vehicles that did have temperature modifying voltage regulators but for the vast majority of 4x4s, 14 to 14.3 IS the average.

Only the D3 and RRS are designed to charge as low as 13.5 and as high as 15.7 as controlled and required by the vehicle voltage monitoring systems.

Cheers
0
FollowupID: 482549

Follow Up By: Mainey (WA) - Thursday, Feb 15, 2007 at 11:21

Thursday, Feb 15, 2007 at 11:21
So reading the various posts above;

You do have to have more power going INTO the battery than what is contained with-in the battery to charge it ?

The problem is the EXACT numbers are now in dispute :((
but as can also be read even these numbers will vary from vehicle to vehicle !!

A bucket of water won't recharge a battery lol
0
FollowupID: 482608

Follow Up By: drivesafe - Thursday, Feb 15, 2007 at 12:26

Thursday, Feb 15, 2007 at 12:26
Hi Mainey, as far as current goes, there is not much difference between types of batteries.

The vast majority of automotive batteries require somewhere between 5% and 10% more current during charging than will be stored. So for every 20 amps needed by the battery, you will need to supply between 21 and 22 amps of charge.

In small dual battery set ups, the additional current is not all that important but once you start getting up in storage size then the additional current requirements should be factored in.

Cheers
0
FollowupID: 482624

Follow Up By: GaryInOz (Vic) - Monday, Feb 19, 2007 at 21:34

Monday, Feb 19, 2007 at 21:34
Charging current overheads vary as a proportion of rate of charge coupled with size of battery.

If you have a 100 ah battery it may take 53 hrs at a 2 amp charge rate (106 ah going in), but it will take 5.5hrs at 20 amp (110 ah going in) These are basic figures off the top of my head, but are pretty representitive.

If you had a 10 ah battery you could reduce the currents of the above example appropriately (ie one tenth), but not the times. (normal batteries)

Some AGMs are designed to take an effective "not limited" charge rate and can be fully charged up to their capacity within two hours (some small 10-15 ah ones in less than 1 hour using a 20 amp charger), it is at these points that you see the "charging rate x time" equations take a bit of a hammering and things get less efficient, but only up to about 20% over .

Notwithstanding, there are other influences that affect a batteries ability to absorb current, such as battery construction and heat, as well as age, etc. There is no "one size fits all" answer only the best solution to a particular set of variables.
0
FollowupID: 483606

Follow Up By: drivesafe - Monday, Feb 19, 2007 at 23:28

Monday, Feb 19, 2007 at 23:28
Hi GarylnOz, if only it was that simple.

AGM batteries in the right situation, can be charged much quicker than conventional wet cell batteries.

Wet cell batteries, for a start, should not take so low that they need to have that amount of amps replaced.

Next, even taking one to as low as 25% State of Charge, will require at least 6 hour to 8 hours to fully recharge these types of batteries.

Just because you have a supply current of 20 amps at a given voltage does not mean the battery will take 20 amps constantly till it’s fully charged.

You will get the bulk of the charge, up to about 75% then the current requirements of the battery will taper off pretty quickly from this point and will continue to drop off as the battery gets closer to full charge.

Cheers.
0
FollowupID: 483640

Reply By: MEMBER - Darian (SA) - Wednesday, Feb 14, 2007 at 09:33

Wednesday, Feb 14, 2007 at 09:33
I've just teamed my Yamaha 1kVA inverter gennie with a 240 volt 3 stage 25A smart charger (Power Saver brand - from ABR - Trader on here). In rough figures, that charger is taking 25 x 12 watts out of my available 900 - in deciding how far to go in the exercise, the gennie will obviously run a bigger charger, but the weight and the cost keep climbing - I just settled on the 25 watter as a practical compromise. The above charger lets you choose between gel and wet and has 3 float voltages. When I run the gennie for aux top-ups in the car, I'll probably have the fridge and the camper's in built charger (50AH deep cycle) all running on the 240 side.
Re the 12V 8A output side - its unregulated - not good I'm told - you could fall asleep in the chair with a beer and then awaken to the smell and sound of an overdone battery ! Regulators for that output might be about $70 - cheaper as an exercise, but my view was that the even though these gennies are quiet (the Yam has the same specs overall as the Honda) the extra $ spent on the 240 plan will take many hours off the running time.
AnswerID: 221604

Follow Up By: disco1942 - Wednesday, Feb 14, 2007 at 13:31

Wednesday, Feb 14, 2007 at 13:31
As I stated in an earlier Follow-up the 12 V output is not capable of charging a battery to any great depth so it is not capable of destroying your battery.

PeterD
PeterD
Retired radio and electronics technician

Lifetime Member
My Profile  Send Message

0
FollowupID: 482383

Reply By: Tony - Wednesday, Feb 14, 2007 at 14:59

Wednesday, Feb 14, 2007 at 14:59
I have a 15amp 3 stage smart charger wired into the camper. Plug the honda into the 240v power inlet, charger goes through the motions charging two battries in the camper and one in the vehicle, fridge switches over by itself to 240.

It takes about 7hrs to charge all 3 battries up before the charger goes to "float" mode.

This is done usually on the third day in one spot, running two fridges, pump, lights etc.
AnswerID: 221667

Reply By: Muddy doe (SA) - Wednesday, Feb 14, 2007 at 18:23

Wednesday, Feb 14, 2007 at 18:23
Many thanks for all the helpful answers and advice.

Best option out of all this is a 25 Amp smart charger which the Honda will handle with ease.

This has certainly rasied some interesting discussion. Gee I love this site!

Cheers
Muddy
AnswerID: 221723

Follow Up By: Member - Norm C (QLD) - Wednesday, Feb 14, 2007 at 22:56

Wednesday, Feb 14, 2007 at 22:56
Sounds like a good choice Muddy. I run a 1KVA gennie and a 25Amp CTek multi stage charger. I now carry four AGM deep cycle batteries (2 in Hilux, one in CT and one for elec motor in boat). When charging with the gennie, I generally only charge till absorbtion stage is complete. At this point battery is probably at least 85% to 90% charged (but this is a guess) and current draw drops to just a few amps. Not worth running the gennie to suck out that final bit of charge. Whenever I have access to 240V mains, I fully charge.

All works great for me.
0
FollowupID: 482535

Reply By: Boxhead - Wednesday, Feb 14, 2007 at 19:35

Wednesday, Feb 14, 2007 at 19:35
Muddy,
from experience my EU10i will not run my 50Amp Xantrex charger on eco mode because of chargers periodic battery analyse then returning to "full" charge after, -- this draws too much current hence overloading gene.
this seems to apply only when battery bank is approx. 70% or less [when u want max. charge]
In hindsight I would go for max. 40 amp charger or EU20I gene
hope this helps
Box
AnswerID: 221743

Sponsored Links

Popular Products (9)