Engel and fridge cooling
Submitted: Wednesday, Dec 24, 2008 at 21:55
ThreadID: 64550 Views:9512 Replies:9 FollowUps:21
I have a 60l engel fridge and freezer. It struggles in high temps and am hoping a fridgie can give me some info. I was told the max delta T a fridge on 134A is something like 43 deg C. So if outside is 35 deg C then can only get around -8 in the freezer. Not sure if this is right as I my freezer in a garage gets way better than that. So firstly is this right??
Engel conditions; fridge under a canopy in back of patrol ute with door open. Cloudy day at 32 deg C but high UV. Slight breeze but not sure how much getting over sides. Very humid when breeze stoops. Day two of trip so everything cold bar a few drinks just put in. Three batteries running at 12.2 volts. After night time temps the freezer down to -9. By 1pm and above conditions freezer down to 1 deg C. Again by early next morning back down to -10 deg C. Setting at around 4 but doesn't really matter as it runs non stop during the day. Fridge only 2 years old.
Is this normal and with the above conditions it simply can't handle it?
Reply By: robertbruce - Wednesday, Dec 24, 2008 at 22:50
heya Austravel,
from first appearences it should run better...but there are so many variables...
i would start by producing the same temp conditions but running the firdge off a 240volt line...
this method discounts any power issues
but a quicker test would be to note how hard the compressor works by klistenning to it when jenny is running it compare to battery...
even when my new 100amp hr agm is fuller than me, there is a differance when my battery charger goes to maintence mode... but three identical batterys with a full guage wire and quality charger, solemoid and regulator should be able to run a compressopr frg
AnswerID: 341305
Follow Up By: oldtrack123 - Wednesday, Dec 24, 2008 at 23:03
Hi IF the battery voltage @ bat terminals is only 12.2 v they are far from fully charged.
Suggest you also check actual voltage @ fridge while running, you could have a substantial voltage loss between bats & fridge.
Low voltage @ fridge could be critical when max operating efficiency is required, also like any fridge they do need good ventilation especially in hot weather.A small fan such as a computer type would assist cooling of the unit.
FollowupID: 608966
Reply By: GerryP - Wednesday, Dec 24, 2008 at 23:27
Hi Austravel,
It should do better than what you describe. It worries me that you say it runs all day. That tends to suggest it may be short on gas. However, it could also be an inefficient compressor or a partial blockage in the gas line (early engels had a habit of blocking the small filter/drier). Really need a fridgie to check pressures/temperatures of the fridge circuit to analyse properly.
Make sure you get full battery power at the fridge and also make sure it is well ventilated to allow airflow over the condenser coil to get rid of the heat.
Gerry
AnswerID: 341311
Reply By: RV Powerstream P/L - Thursday, Dec 25, 2008 at 05:49
You cannot compare your freezer in the garage at home to any fridge under a canopy of a ute.
The biggest problem with fridge statistics is the misuse of the data.
Telling you that a fridge will run at 2.8A is only half the story as that is at 25oC.
As the temperature rises the compressor has to work longer to get the extra heat out of the wall of the unit to the extent that some fridges will run 24/7.
There is only a few fridges have enough insulation in them to make them efficient and they are designed and built in countries that understand the high ambient component and do not build to a European influenced standard.
One such fridge is the Trailblaza.
It certainly appears that your batteries are far from charged and you are using a lot more power than you think and your temperature under the canopy is not what you think it is if you were citing outside temperatures.
Ian
AnswerID: 341318
Reply By: Member - Phil G (SA) - Thursday, Dec 25, 2008 at 08:53
Is the fan working? One of my Engels is the current series and fan stopped working and it cycled more. The fan was OK, so I assume there was a problem with the circuit supplying 24V to the fan. Rather than get it fixed by Engel, I now run a separate 12V fan via a switch and just leave it turned on during the day.
I have also added extra insulation to both my engels by sticking high density foam mat all around the outside and underneath. Running my old Engel as a freezer, it was also cycling most of the time and was getting down to 12.5 degrees. Since adding the insulation, its now getting down to 14.5 degrees.
If you want to add insulation, I suggest using the stuff sold by SuperCheap - cost $22 for 4 mats, and it is more robust than many other mats I looked at.
Image Could Not Be Found
AnswerID: 341330
Reply By: Member - 1/2A - Thursday, Dec 25, 2008 at 17:39
Yes I had an Engle 60L and that also battled at temps above 40 deg C and ran most of the time. I now have 2 Bushman Fridges and I run the one as a freezer at -17 deg C and the other as a fridge 0 deg C and both of then use a lot less power than single Engle 60L.
The larger Engles use a lot of power and are running constantly all day in temps above 40 deg C
AnswerID: 341359
Reply By: Austravel - Friday, Dec 26, 2008 at 00:12
Thanks Gents for all the suggestions. Voltage is lowish as it was running for over 24 hours after setting up camp but still at an acceptable level. Temp quoted was under canopy. Forgot to say it has an after market fridge bag.
Will check the voltage at the fridge itself. 12.2 V was at the solar regulator where all three batteries join. Will also double check the fan but believe it was running.
AnswerID: 341379
Follow Up By: oldtrack123 - Saturday, Dec 27, 2008 at 18:24
Hi Ausrtavel
"Will check the voltage at the fridge itself. 12.2 V was at the solar regulator where all three batteries join. Will also double check the fan but believe it was running."
What capacity solar panels do you have??
An engel running on freeze [MAX] will typically draw in excess of 100A/HS PER 24 HRS,ie IT WILL REDUCE 2X100AH BATTS TO 50% CAPACITY IN 24HRS
AS you move it back to a warmer setting the power [amp/hr ]draw decreases , usually running it around 4degs will draw 25<50 ahs per day DEPENDING ON HOW OFTEN YOU OPEN & what warm loads you put into it.
The unit does NOT actually draw more current @ low voltage it just operates so inefficiently [ the swing motor cannot make a full stroke due to low voltage] that it will not reach a set temp & switch "off "so it will run for much longer times doing no usefull work & thus run the bats down.
ANY compressor fridge is a problem with power if you are sitting down for a few days unless you have adequate means of charging the bats which as others have said should be deep cycle types to withstand the hard work.
For long term camping 3ways are often the best way to go. I run both types & have 200a/hrs bat capacity & 200w solar panels & have often had to move frozens to the 3way during poor weather.
FollowupID: 609162
Follow Up By: oldtrack123 - Saturday, Dec 27, 2008 at 18:42
IF you are getting 12v+ AT the fridge terminals & with no signs of heating or excess temp at plug [ which would indicate poor connection & loss of voltage there] VOLTAGE IS NOT THE PROBLEM .
BUT if voltage is 11.5v or lower then that is most likely the problem.
AS said previously you need to protect the fridge from high ambient temps & get rid of the heat from the radiator fins as much as possible.
FollowupID: 609166
Follow Up By: Austravel - Sunday, Dec 28, 2008 at 11:39
Thanks Oldtrack,
Set up is one 57 litre (approx 60) combi fridge and freezer, Engel. Three NZ70 cranking batteries in parallel and I can and do bring in the NZ70 starting battery. So for a day or so I have 4 batteries in parallel until the voltage drops to low 12 volts. I have one 80 watt panel that I only use if staying for more than 3 full days. Otherwise I just run off the batteries. Voltage can get down to mid to high 11 volts but that's after 3 days and unusual. Generally voltage is down to 12 as a min.
Voltage just before plug into fridge is approx 0.4V below battery voltage. This will be due to fuses and standard engel plugs. Not sure what it is after the last engel plug it's a bit hard to get access.
I didn't realise ths particular motor wouldn't increase current draw with a decrease in voltage. My understanding from W=VxA is that amps will increase if volts drops to ensure constant energy to the appliance. Are you saying with the Engel that current draw remains constant so wattage drops??
FollowupID: 609255
Follow Up By: oldtrack123 - Sunday, Dec 28, 2008 at 17:38
Hi Austraveller
"I didn't realise ths particular motor wouldn't increase current draw with a decrease in voltage. My understanding from W=VxA is that amps will increase if volts drops to ensure constant energy to the appliance. Are you saying with the Engel that current draw remains constant so wattage drops?? "
W=VA could be interpreted as you have done but that is true only if you know the actual v & amps draw. with out complicating it too much I''ll use a simple electric heating element as an example .
IT has a reasonably constant resistance of 1ohm ,apply 12v & the current will be 12amps . w= 12v x12a =144w.
Drop the voltage to 10v the resistance is still 1ohm but the current drops to 10amps,10v x10amps =100w.
IE a16% voltage drop gives 30.5% loss of power. This why cable size is so important in low voltage systems cable voltage loss can lead to greatly reduced wattage to do the work.[ especially with 3way fridges on 12v]
NOW a little complication is that this does not hold true for electic induction motors under all conditions, BUT THE ENGEL SWING MOTOR IS not AN INDUCTION MOTOR,It is a selonoid type action whose current draw is determined by the#1 applied voltage,#2 the reactive resistance of the winding [ due to normal wire resistance & the magnetic effect of the iron core ,in simple words in case there are any purists reading] & #3 finally the supply frequency. # 2 & #3[which give what is near enough the equivalent of restance areconstant]
SO as in the heater the lower voltage will give actually a lower current & the WATTAGE AVAILABLE TO DO THE WORK ie PUMP REFRIDGERANT IS LOWER than the name plate rating which is only correct @ the specified voltage.
I know this was looong but could not see any way of shortening it.
"QUOTE This will be due to fuses and standard engel plugs. Not sure what it is after the last engel plug it's a bit hard to get access UNQUOTE"
You can get a reading under load right @ the last plug by carefully sticking a pin into each cable & reading from them, also note the plug may have high contact resistance is there any sign of heat at the plug.?
If all is ok then all you can do is improve ventilation, insulate even more, put in coolest possible area.
As someone else suggested it could be faulty[ loss of gas , clogged line etc , the easy way to check is run it on 240v .
FollowupID: 609281
Follow Up By: Austravel - Sunday, Dec 28, 2008 at 19:57
Hi OT,
Thanks for the electrical lesson. So when or for what equipment do you see current increase as volts decrease to ensure wattage is the same?
Sticking pins in is what I did to get the 0.4v drop. The plug seemed ok temp wise. However I intend trying to get access after the plug. Strangely there is a 0.8v drop when using the earth wire inside the cabinet. Ie pin in positive wire before plug and earth wire from motor to cabinet. Now I believe there's a bit of trickery in the electronics to invert the voltage. Not sure if this is why I'm getting such a voltage drop using the earth wire at this point.
That's the thing when using 240v or over night with the fridge running flat chat on 12v it will pull down to -18 to -20 deg C. So my thoughts where that either the compressor can't keep up in the heat, ie to many losses through the cabinet. Or it can't remove the heat from the condenser in high ambient temps efficiently.
Re-reading the first post I didn't put this in. What's it about assuming.
FollowupID: 609309
Follow Up By: oldtrack123 - Sunday, Dec 28, 2008 at 22:55
Hi Aus
"So when or for what equipment do you see current increase as volts decrease to ensure wattage is the same? "
In simple circuits rarely ,however electronic circuits can be designed to do just that, if required, to cope with normal voltage fluctuations, but obviously have a design limit .ie If voltage falls to zero then there is no voltage to drive the system.
A simple devise that was used for many years to maintain near constant current[not an increase in current]where special iron filament bulbs whose resistance increases in a near linear form ,over their designed range ,ie as voltage increased current increased , resistance increased current decreased. similarly if voltage dropped, current dropped, Resistance dropped current increased.
This can be seen in any light bulb, measure its cold resistance & do a watts calculation you will find its actual wattage from those reading is many times its rated wattage as it heats up the resistance rise rapidly to give its final working temp & wattage This massive initial surge current is the reason light bulbs OFTEN fail @ switch on.
AC equipment incorpoating any form of ferrite [iron ] have an inductive effect which has a limiting factor on current, the effect is also frequency dependent ,@ lower frequencys more current will pass or be drawn by the devise, higher less current.
Electric INDUCTION motors current changes according to load[higher load = higher current] but if voltage is low[ LOW POWER OUTPUT] & they loose speed they will not generate what is called back emf [voltage ] & their current will rise dramaticaly Again measure the resistance of any motor, ac or dc,& do watts calc,YOU WILL SEE A SIMILAR RESULT TO THE LIGHT BULB.
Now back to your orignal problem, I wonder what the temp in the vechicle is ,the efficiency of the refrigerant certainly drops off with temp rise as it leaves the condenser[ thats why good cooling of the condenser is so important on ANY fridge. I think from memory that most compressor fridges with new gas requirements start to loose their ability around 40deg C & CERTAINLY THE RUNNING TIME WILL ENCREASE DUE TO THIS LOSE OF EFFICIENCY AS WELL AS DUE TO HAVING TO COPE WITH HIGHER CASE TEMPS ETC.
MY Engel has coped with near 40degs but I have insulated with 25 mm of polyeurethane all round[ top, bottom, sides.]
We did a trip wth temps in that range many years ago around Aus in an old toyoata with no aircon OUR one saviour was icy pole ice blocks with which we could have made a fortune as we pulled up @ such place as HAMMERSLY GORGES , the Olgas etc.
We were approached from many wanting to know where we got our ice blocks, did we have any to sell etc , all in our ENGEL
I do believe the now illegal gas may have been more efficient in high temps.
FollowupID: 609331
Follow Up By: oldtrack123 - Sunday, Dec 28, 2008 at 23:29
Hi Aus
"Strangely there is a 0.8v drop when using the earth wire inside the cabinet. Ie pin in positive wire before plug and earth wire from motor to cabinet. Now I believe there's a bit of trickery in the electronics to invert the voltage. Not sure if this is why I'm getting such a voltage drop using the earth wire at this point. "
I'll have to see if I can find my old wiring diagrams to check that out but from memory neg & earth should be common & that may be the answer [a fault in the plug or socket].
WHEN your 80 the memory does loose a few things.
FollowupID: 609334
Follow Up By: Austravel - Monday, Dec 29, 2008 at 23:20
Hi OT,
Would appreciate it if you can have a look at a wiring diagram and let me know if it is a common earth. If so then either there is a large voltage drop across the plug into the engel or losses through out the inverter etc, etc.
FollowupID: 609455
Follow Up By: oldtrack123 - Thursday, Jan 01, 2009 at 12:58
Hi Aus
I can not find my Engel diagrams , must have put them in a safe place during a senior moment.
I have checked on my 2 Engels & found there is no direct [common] connection between frame & neg. There does appear to be a capacitor between frame & neg which could be responsible for the reading you are getting[ very low leakage will show on modern high sensitivity meters.]
Back to base possibilties are:-
loss gas, a crackedpipe as most likely cause ,it can happen with severe vibration.
Though you appear to have sufficient voltage does it have healthy 50cycle/hertz hum. could indicate faulty inverter.
Somtimes if stored for a long period the the system can get a blockage.
Inadequate cooling of the condensor.
faulty lid/ door seal .
SIMPLY TOO HOT TO COPE bearing in mind that performance does fall off@ high temps.
A faulty swing motor
FollowupID: 609770
Follow Up By: Austravel - Thursday, Jan 01, 2009 at 14:04
Thanks OT,
I'm not as senior as you and trust me have far to many of those moments lately.
Thanks for all the suggestions, some I've checked but will work through the rest. Yes the hum sounds ok, even though my technical field is mechanical (thermo, energy etc) it sounds ok to my non electrical ears.
The more I read and consider I feel it's more about not coping. I think the thermal load builds up through the day and it simply can't get rid of it. I'm sure if I could keep the voltage up and concentrate on cooling a bit more it would help. As would making sure it reached min temps over night but that's a catch, uses more current doing so.
Will let you know what I find.
Thanks again for the help.
FollowupID: 609774
Reply By: Best Off Road - Friday, Dec 26, 2008 at 06:44
Something radically wrong.
I have a Waeco 80, which is equally as poorly insulated as an Engel, and in 40+ it holds at least -10 in the freezer and at the warmest point of the fridge section (up high at the far end) it was +6. This was prior to fitting a bag, so it should do better now.
In this kind of heat it runs 100% of the time without a bag. Yet to try it with the bag in such heat.
This is not a brand war, because I simply do not believe Waeco is any better or worse than Engel. I've owned both and been reasonably happy with them. Next time I'll buy a fridge with better insulation, but I'm in no hurry.
Jim.
AnswerID: 341385
Reply By: Member - bungarra (WA) - Friday, Dec 26, 2008 at 10:57
G'day Austravel
We run 2 Engels...a 60 L as a fridge very constant at 2 to 3 deg...and a 39L as a freezer......cycles between -9 and -14 subject to the ambient.......and yes ambient has been up in the very high 30's.
Never an issue BUT we have good air circulation around them and also heavy cables with no voltage drop (as measured at the fridge whilst running)..also 200 Ah AGM suplying them and well maintained and charged (alternator and solar...never carry a genny)
before spending money on a "fridgie" seems to me that you need to make certain you have a good air circulation and correct voltage at the fridge when running...12.2V is too low....the lower the voltage the higher the amp draw and the quicker the batteries run down..you end up chasing your tail
maybe you might have a fridge problem but seems more like your voltage and conditions...I would be looking at them first
VKS 1341
AnswerID: 341393
Follow Up By: Austravel - Friday, Dec 26, 2008 at 12:24
Hi Bungarra,
At 12.2V the current draw will be higher but I thought the Engel's could handle much lower and still function respectably. Yep it reduces battery life but it's a trade off.
Here's my situation. Sitting in the one spot for 3 days, bar a quick run to check the pots. Approx 300 Ah in 3 cranking batteries, I know not the best but let's assume this is approx right for this case. I even bring in the main cranking battery for a bit, so that's 4 NZ70's I carry. Over cast sky so no use putting out the panel. Not using genny as NP. Therefore after day 1 battery voltage is down to 12.??V
How do you keep the batteries charged under these circumstances? Plus are you saying that the Engel will run colder when bat voltage is at max?
FollowupID: 609048
Follow Up By: Austravel - Monday, Dec 29, 2008 at 23:18
Hi Bungarra,
Just re-read your post and notice you say you heavy cables with no voltage drop. Where did you measure the voltage, after the plug into the fridge? If so how did you do that?
Did you use the supplied engel cables? I used both the one with the two inline fuses and female socket and the one with the male socket to the plug for the fridge. This setup losses around 0.4V. Might be worth taking it all out but even by removing the female/male plug I can't see it dropping back to zero in my case.
FollowupID: 609454
Follow Up By: Member - bungarra (WA) - Monday, Dec 29, 2008 at 23:56
G'dday Austravel
Over the years I got sick of all the experts that sold me 12v gear but never really used it or understood it (and left me with hot beer and no power) and so I made a test box so I could better understand what the hell was really going on with current draw, voltage etc of the all the various accessories.
purchased a little black (can get them in grey) plastic box about the size of 2 cigaret packets...empty things used for a multitude of uses..but cannot think what they call them...get them from Dick Smith outlets
anyway I purchased a volt meter and an amp meter and set them into the top of the box. On one end of the box I put a male plug to receive the power and fed it through the gauges and out to and around the other 3 sides I arranged various outlets...2 pin round, engel outlet, ciggaret outlet, anderson, and another outlet that I cant think what it is called at the moment.
the idea was that whatever the acccessory plug arrangement had that I wanted to test had the ability of drawing through my test box....amazing how many times it has been dragged out over the years when campers we have met start telling of their 12v power woes..havent been stumped yet in putting inline for them and at least they can see actuals..not theorys.
So in actual test mode there was still the supplied factory cord between the test box and the accessory under test..........but only that length.........I tapped into the supply line at the far end of the supply discharge...in other words where the acccessory was going to receive the power...furtherest from the battery......I believe the actual voltage drop in the 1 maybe 2 meters of accessory cord supplied was irrelevant and so have never taken that into account
hope that might help you...
VKS 1341
FollowupID: 609459
Follow Up By: Austravel - Tuesday, Dec 30, 2008 at 10:18
Hi Bungarra,
Thanks for the reply.
"So in actual test mode there was still the supplied factory cord between the test box and the accessory under test..........but only that length.........I tapped into the supply line at the far end of the supply discharge...in other words where the acccessory was going to receive the power...furtherest from the battery......I believe the actual voltage drop in the 1 maybe 2 meters of accessory cord supplied was irrelevant and so have never taken that into account"
I guess in testing like this it assumes the plug into the fridge is ok. Not knocking your process it's just in my case this might be the drama, so will have to try and test the voltage after this point. Your right though, pull everything down to it's simplist and test step by step.
I'll need to check into AGM's when I next change my batteries.
By the way, love your rig set up.
FollowupID: 609497
Reply By: Member - bungarra (WA) - Saturday, Dec 27, 2008 at 10:36
G'dday Austravel
I think the first clue you have given us to help solve your problem is ...."so that is 4 NZ70's that I carry".....
That gives a better understanding of your problem because that is not ..."300 Ah in 3 cranking batteries"....that you mentioned as an assumption as approximate for this case.
You dont have 100 ah in each of your NZ70's.......Cranking batteries are designed to discharge a considerable amount of energy over short bursts to crank the battery and each successive discharge ( starter motor or for example a fridge) reduces available voltage for the next draw..........that is why they are measured in CCA..........they should last thousands of cycles used as starting batteries (2-5% discharge)...and may last only 30-150 cycles if deep cycled and running them down to 12.2 v is not doing them any good at all.
Deep cycle batteries are designed to deliver amps over a period of hours and maintain a steady voltage..........hence they are more effecient at supplying and maintaing a constant power draw..designed to discharge down as much as 80% time after time
An amp hour is one amp for one hour. or 10 amps for 1/10 of an hour and so on. So a fridge pulling 3 amps and used for one hour is 3 ah used or 1 ah used if run for 20 mins.
Back to your fridge...being an Engel and depending upon its age and size they seem to use a draw of between 2.5 and 3.5 amps.....so if we use 3 ah as an average and work on a high ambient maybe a safe guestimate is running 75% of the time...so 24 hours X 3 ah X0.75 = 54. So if you had a 100ah deep cycle it is now roughly 50% discharged but still supplying a voltage of probably 12.4 or higher depending upon its condition.
a cranking battery of N70Z size would by now be under voltage and over discharged.....and chasing its tail as the current draw would be higher as the voltage droped.
As I stated in previous post I run a 60L fridge and a 39 L freezer on 2 x 100ah AGM deep cycle batteries and are usually into day 3 before I have any approaching power supply issues and obviously longer if the ambient is down ...my draw is closer to 5ah with both runing and using the same figures I used for you gives 90 used in a 24 hour period......in actual fact I dont recall ever using that amount and so the 75% duty cycle is probably very conservative
Suggest you also monitor the fridge temperature to ensure you are not running colder than is necessary...that will help conserve energy reserves
There are a lot more people on here with greater knowledge of this situation than me but the bottom line is that from what you have stated it is your choice of batteries that is your problem
VKS 1341
AnswerID: 341480
Follow Up By: Austravel - Saturday, Dec 27, 2008 at 12:31
Thanks for the detail. I've never gone down the path of deep cycles. If it's a true deep cycle and not a hybrid then recharging times are an issue. I believe even an AGM deep cycle has a much longer charge time than the cranking battery. If it's charging quickly it's most probably a hybrid. I've heard the same about discharging cranking batteries and longevity. However the last lot of Cat cranking batteries lasted around 10 years of deep discharges. I'm sure they can fail quicker but maybe the better ones can handle it for longer.
Mine is a 60l combi and I think amp draw is over 4amps.
Are you sure at 50% discharge your battery is still at or over 12.4v?
Do you find it takes a long time to charge your deep cycle agm?
FollowupID: 609140
Follow Up By: Member - John (Vic) - Saturday, Dec 27, 2008 at 20:31
I thought AGM's accepted charge faster than lead acid batteries??
FollowupID: 609181
Follow Up By: Member - bungarra (WA) - Saturday, Dec 27, 2008 at 22:38
Hi Austravel
havent kept specific records of all the settings but what I can tell you that my 2x100ah AGM are currently showing 46% SOC and 12.06V.
As for charging time quite frankly I dont take a lot of notice....they are either being charged by the alternator whilst driving or the 4 x 75 watt panels do the job...never had an issue to date
VKS 1341
FollowupID: 609198
Follow Up By: Austravel - Sunday, Dec 28, 2008 at 09:32
Thanks Bungarra.
John Vic), I've been told that cranking AGM's charge very quickly but deep cycle AGM's are typically slow. This is due to construction. But just because this is what I was told doesn't make it right hence my question to Bungarra.
FollowupID: 609238
Follow Up By: oldtrack123 - Sunday, Dec 28, 2008 at 23:15
Hi Aus
Bungarra's post 9of 9 is very good [except for the current draw encreasing as the voltage drops . The actual current demand of the fridge {amps} will decrease but due to inefficiency the total draw { amphrs } from the bat will encrease.]TAKE NOTE OF HIS COMMENTS TOO.
FollowupID: 609332
Follow Up By: Member - bungarra (WA) - Tuesday, Dec 30, 2008 at 00:05
oldtrack123
thanks for picking me up on my current draw explanation
VKS 1341
FollowupID: 609460