So what is the right time selection for the UO stage?
I recommend to follow this procedure:
Discharge your battery to about 50%.
Wait for the ambient temperature to come down to around 25 degrees.
Select the 8 hour UO time limit.
Select 14.7V for AGM.
Have the charger's temperature sensor mounted on the battery surface.
Disconnect any loads from the battery.
Aim for a C/5 or C/4 charging rate which is the full power mode on your 45A charger, for your 210Ah combo.
Connect a voltmeter across the battery terminals.
Connect charger to the batteries and turn on the charger.
Jot down the first time stamp, when the meter reading has reached 13.8V, which can take an hour or so.
Listen/watch the fan/yellow LED to turn off/change colour to green, which can be another hour or so.
Jot down this second time stamp.
Subtract your first time stamp from the second one, and add one hour.
If the result is less than four hours, select 4 hours for the UO timer.
If the result is more than four hours, select 8 hours for the UO timer.
Note if you regularly discharge your batteries to more than 50% to 60%, I recommend to select the 8 hr limit, regardless of the
test result above.
A little caution:
because you've got a high rated charger, which lets you recharge your battery in the shortest possible time at the maximum recommended C/4.5 rate, it is definitely advisable to use the battery temperature sensor.
If for whatever reason you don't have this sensor, I recommend to reduce the boost charge setting from 14.7V to 14.4V during summer.
Be aware that the float voltages will be out as
well without the T/S connected. Unfortunately these can't be tweaked.
Hope this helps.
Best regards, Peter