Generators and Earthing

Submitted: Friday, Apr 08, 2011 at 22:41
ThreadID: 85520 Views:13504 Replies:5 FollowUps:11
This Thread has been Archived
I noted a while back a lot of discussion on Generators powering caravans, earthing, RCD's, and the MAN wiring methods.

A comment that was made to the effect that Australian regulations do not allow the grounding of a generator.

I am curious to know from thiose that know why we are not allowed to ground generators in Australia (not that I want to I am simply curious).

Ken
Back Expand Un-Read 0 Moderator

Reply By: Alllan B (Sunshine Coast) - Saturday, Apr 09, 2011 at 00:12

Saturday, Apr 09, 2011 at 00:12
Hi Ken,

As I recall, the Australian/NZ standard does not prohibit earthing of portable generators but it does state that it is "neither required nor recommended".
I have not seen authoritative explanation for this nor am privy to the considerations of the engineers responsible for the Standard.
I would however guess that they consider that it is better to leave the entire installation "floating". As the earth pin of the generator outlet socket is connected to the frame of the generator this would ensure that all exposed metal of the system would be at equipotential.

In my early days at Woomera Range we used many mobile 240v generators for supply to remote instrumentation installations. The earthing conductors of the load installations and the frame of the generators were always bonded but the neutral was not connected to earth. The system "floated" but all exposed metal was at equipotential. An earth stake was always employed but for the purpose of assisting to reduce RF interference rather than electrical safety. Mind you, with the usual dryness of the soil I was never confidant that the stake was of much value.

I would be pleased to hear from anyone with authentic knowledge of the reasons for the Standards clause.

Cheers
Allan

Member
My Profile  My Blog  Send Message

AnswerID: 450744

Follow Up By: Alllan B (Sunshine Coast) - Saturday, Apr 09, 2011 at 10:20

Saturday, Apr 09, 2011 at 10:20
Perhaps I should add that it may be impossible to NOT ground a portable generator.
If the generator has an exposed metal frame then simply placing it on the ground will "ground" it. Perhaps not very well, but it is grounded nevertheless. If the soil, concrete or whatever is wet then it may create a very effective grounding.
Even if the gennie has rubber feet, contact between the metal chassis and "ground" may be effected due to unevenness etc allowing direct contact.

Accordingly, there is no point in prohibiting "grounding" or earth electrodes if it can easily be created inadvertently. It can do no harm and may even be beneficial in some circumstances but is not prescribed as being necessary.
Cheers
Allan

Member
My Profile  My Blog  Send Message

0
FollowupID: 723236

Follow Up By: paulnsw - Saturday, Apr 09, 2011 at 10:52

Saturday, Apr 09, 2011 at 10:52
The other issue to consider which renders grounding next to useless is small portable inverter generators are like 12/240V inverters, both legs are hot, you don't have an active and a neutral.
0
FollowupID: 723239

Follow Up By: KenInPerth - Saturday, Apr 09, 2011 at 11:12

Saturday, Apr 09, 2011 at 11:12
thanks Alllan (with 3 L's ??)

Adding something else in, I believe it was also said that you do not tie the Neutral to the Earth back at the source as you do in House wiring (MAN) where the Earth and Neutral are tied together back at the main distribution point. Or maybe it was that you do not tie them together in the Caravan (load) wiring as that would be done externally if you were on a powered van site.

As I see it you would have to tie the Neutral of the Generator to the Frame and all exposed conductive components and the Earth of the power outlets and then Earth Stake it to get a true MAN system and then an RCD would work properly AS LONG AS you had an effective Earth system.

HOWEVER, I think you probably hit the nail on the head when you said "with the usual dryness of the soil I was never confidant that the stake was of much value" assuming it is moisture in the soil that makes our earthing system work. In many cases the earth stake would be ineffective.

The paper referenced by Notso in this post at a brief glance appears to suggest you at least tie all exposed conductive stuff together which would be the frame of the caravan or whatever and the gen set components so at least all that is at equipotential, although it seems to be more on Welding applications, but the same reasoning would apply to anything. At least that way you cannot get yourself between 2 conductive items that might be at different potential and become a conductor yourself.

If the system was left "floating" then it would seem the only danger to you is if you get yourself between the "active" and the "neutral" themselves (or call them L1 and L2 if you like) - if you were to come in contact with one or the other on their own you would not be affected as there is no path to Earth (like a bird sitting on a single power line). So then in the case of faulty wiring or a faulty appliance if you came into contact with the "active" it would be "safe".

I note paulnsw just posted about not having an "active and neutral" as such - well yes that applies to any floating system that has no external reference - I am only using active and neutral to differentiate the wires.

Ken

0
FollowupID: 723241

Follow Up By: Alllan B (Sunshine Coast) - Saturday, Apr 09, 2011 at 11:32

Saturday, Apr 09, 2011 at 11:32
Re; "thanks Alllan (with 3 L's ??)'
Yes Ken, I carry a spare. LOL
Cheers
Allan

Member
My Profile  My Blog  Send Message

0
FollowupID: 723244

Follow Up By: Alllan B (Sunshine Coast) - Saturday, Apr 09, 2011 at 12:45

Saturday, Apr 09, 2011 at 12:45
Ken, The ideal electrical supply system is "Fully Isolated" where there is no reference between the live conductors and "ground" or the frame. This is how portable generators and inverters are constructed. In the case of a single phase system there is therefore no "neutral" so the convention is to designate the conductors as L1 and L2.
In the case of a reticulated system as we have in towns it cannot be assured that the system could be maintained as "Fully Isolated" due to unintentional (or otherwise) connection between the live conductors and ground. This could be as simple as some leakage due to moisture in an installation or connected appliance. Accordingly it was adopted that one line be earthed and designated as the "Neutral" as it would be at ground potential. For system reliability and reduced impedance of protective conductors, the MEN (Multiple Earthed Neutral) system was introduced where the neutral was connected to the earthing system at each installation. In addition an earth electrode is connected at each installation in order to maintain minimal potential difference between local ground and the local neutral/earthing system.

As a portable generator is limited to a small local installation then there is a better chance of keeping the system isolated so earthing the neutral is less desirable. Nonetheless it is always possible for faults to develop in either the gennie, the cabling, or connected appliances so a protective earthing system is required to ensure equipotential of all exposed metal. It is possible to postulate all manner of faults which can reduce the integrity of the system but normally it will require two such faults simultaneously to present a hazardous situation. Unfortunately the first of such faults could pre-exist without becoming apparent until the advent of the second fault which may be bodily contact with a conductor.
In such a system, fully isolated with equipotential bonding, there is no reference to ground and an earth electrode will provide no real benefit. At the same time it will not compromise the system.

Certainly the incorporation of RCD protection is of benefit but it needs to be properly installed. A simple plug-in type will not provide full protection. This subject is complex and I do not wish to go into it here.

Cheers
Allan

Member
My Profile  My Blog  Send Message

0
FollowupID: 723249

Follow Up By: KenInPerth - Saturday, Apr 09, 2011 at 13:32

Saturday, Apr 09, 2011 at 13:32
Thanks Allan with a Spare L

Incorrectly I was using MAN meaning MEN in my comments - thanks.

That has truly satisfied my curiosity. From what I have read generally sniffing around this subject I would imagine there are a lot of incorrect installations out there and worse a lot of people that may believe they are protected with an RCD when they are not .......

So I guess the bottom line message is if you want to use a Gen set with RCD protection go get it done by someone who knows how to do it properly for your specific situation.


Ken
0
FollowupID: 723254

Follow Up By: KenInPerth - Saturday, Apr 09, 2011 at 13:57

Saturday, Apr 09, 2011 at 13:57
Alllan - FYI - I found this in an article on safework.sa.gov.au - and for those out there think that pushing the test button on an RCD means it is protecting them well that is not necessarily the case. I have seen that misconception floating around also.


Example of portable generator problem

At a major construction project 15 portable generators brought on site by subcontractors were tested by the project managers as a normal part of site safety procedures.

IN ALL CASES THE RCD PROTECTION DID NOT WORK because the
internal wiring connections within the generator unit, but outside the RCD,
were incorrect.

In this case the test button functioned normally because the test button only
tests the tripping mechanism of the RCD not the full wiring of the generator.

Note that the RCD itself was not faulty, the problem was the connections
between the RCD and the generator.



0
FollowupID: 723258

Reply By: gbc - Saturday, Apr 09, 2011 at 07:15

Saturday, Apr 09, 2011 at 07:15
I'm not a sparky.
We also used to earth our gensets, but have since been told not to by our whs rep.
The reasoning behind this (using metal framed gensets) apparently, is that if an incorrectly wired lead or tool is accidentaly plugged in while the genset is earthed, the whole frame and whatever it is sitting on (trailer in my case) can become live. A sparky will be able to explain it properly.
I've got another 8kva genset on backorder at the moment, and apparently it is RCD protected without the need for earthing. I do not know how this is achieved, but we will be testing it, and if it proves to be successful I'll sleep better at night. We use gensets constantly and I am always aware of the potential danger associated with them.
Plastic framed gensets like tourists use are potentially much safer in this regard simply because they are shrouded in a non conductive material.
AnswerID: 450751

Follow Up By: Bonz (Vic) - Saturday, Apr 09, 2011 at 08:56

Saturday, Apr 09, 2011 at 08:56
gbc, the real danger isnt the frame of the gen-set, but use of tools, extension leads etc. If the gen set frame is earthed, then the voltage it produces is referenced to the earth/ground. If someone hooks up an incorrectly wired lead then any tool connected to it that it not double insulated (which is rare these days) will be "alive" with reference to the ground, and someone holding it can get a shock.

An earthed gen set is safer than a non earthed one as not only is the gen set equipotential but it is also equipotential to the ground/earth. But its only the gen set that is safer.

The RCD works by measuring the current in the active and the neutral and summating them. If there is a residual (or leakage), i.e. one is greater than the other, the RCD trips. The leakage is usually used by the person getting the electric shock.
.
Time is an illusion produced by the passage of history
.

Lifetime Member
My Profile  My Blog  My Position  Send Message
Moderator

0
FollowupID: 723229

Follow Up By: KenInPerth - Saturday, Apr 09, 2011 at 11:47

Saturday, Apr 09, 2011 at 11:47
For an RCD to work on a Gen Set such as GBC is waiting for I can only assume they have tied one line to the Earth pin of the supply sockets so the whole system has an Earth reference (in other words it is not a floating system any more but a MAN system like house wiring).

All the RCD's I know about rely on an imbalance of current as Bonz indicates - as long as the same current is flowing in both lines (call them L1 and L2 rather than active and neutral) then the RCD will not trip.

For it to trip there has to be a leakage to a 3rd reference point (the Earth in a house system) such that if you get between the Active in a normal house and you are sufficiently in contact with the Earth (be it the metal case of an appliance or bare feet on the floor) you will cause an imbalance in the current in one line as some of the current is flowing through you to Earth and not going back the neutral line to the source. Hence the RCD will trip due to the imbalance. Think of it as a water pipe with a leak along the way - what you are pumping into the pipe is not what is coming out the other end as you are losing some water along the way to a 3rd point - the ground.

HOWEVER if you get yourself directly between the active and the neutral wires and you are isolated or well insulated from Earth, you will not trip the RCD as there is no "leakage" to Earth. All the current flowing will pass through your body from the active to the neutral and the amount of current in both lines will be the same - there is no imbalance as there is no "leakage" to Earth.

This second case is the danger in a floating system - you can put an RCD at the source (the Generator) but if you have no 3rd point of reference for current to leak to there will never be an imbalance of current and the RCD will not trip. At the same time though, in a floating system you are not at risk by coming into contact with either of the lines L1 or L2, only if you get between them somehow (and the RCD will still not trip and protect you). This could be due to say a faulty appliance where one line has come into contact with the metal casing (and and you manage to come into contact with the other line somehow - you will be directly between the 2 lines.







0
FollowupID: 723245

Reply By: Notso - Saturday, Apr 09, 2011 at 08:13

Saturday, Apr 09, 2011 at 08:13
There is an iteresting read here

WTIA Paper

It is a treatise on the earthing or not of portable gensets.
AnswerID: 450755

Reply By: Member - Joe n Mel n kids (FNQ - Saturday, Apr 09, 2011 at 09:26

Saturday, Apr 09, 2011 at 09:26
"Generators & Earthing" is like asking about "Fitting Air Bags" ....
It is so funny as some really get fired up about it all, i also can not make head or tail of it as so many people claim to be experts and what they say is official and bla bla bla and most quote from something so it is the final word but it still seems to be so many opinions as to why and how ........
Maybe it is something for the Mythbusters to bust .......... and settle this once and for all ...
Cheers
Joe
AnswerID: 450760

Reply By: ob - Saturday, Apr 09, 2011 at 11:11

Saturday, Apr 09, 2011 at 11:11
Not sure as to the effectiveness of an earth stake but an ex mine site diesel gen set came with an earth stake. The unit is an open frame skid mounted genny which if sat on the ground whether wet or not would still provide some earthing potential, however the powers that be decreed that an earth stake was to be used. As we all know mine site safety personal can be rather anal about procedures and probably quite rightly so.

ob
AnswerID: 450762

Follow Up By: KenInPerth - Saturday, Apr 09, 2011 at 11:17

Saturday, Apr 09, 2011 at 11:17
Yes

I am not sure about the theory of "Earth" and how much it relies on moisture as well - all my theory says most soil is not a good conductor and requires moisture to make it more conductive.

But it generally must have some conduction under all circumstances but if I was relying on it for an RCD to work I would rather be on wet ground than dry ground.

Ken
0
FollowupID: 723242

Follow Up By: skmaint (WA) - Saturday, Apr 09, 2011 at 20:52

Saturday, Apr 09, 2011 at 20:52
ob,

We are running 14 x 40Kva gensets & 3 x 20 Kva gensets on mine site and as you said all the powers to be, state they have to be earthed to an earth stake.
They are also tested & tagged every quarter
Wether it is right I don't know, I am a Heavy Duty Fitter not an electrician.

Cheers
Simon.