Saturday, Apr 13, 2013 at 22:06
"specifically about the voltage from 2 x parallel 150w 12v in shade dipping below the minimum for the mppt controller"
The Vmp (max power voltage) of 12V panels is typically around 18V, plus or minus. They vary a bit. Vmp is the max power voltage of the panels and the MPPT reg will try to hold the panels at that voltage and take the resulting current. That is Maximum Power Point Tracking. Your proposed MPPT reg will track the Vmp if the panel voltage it sees is in the range 15V to 37V (in a 12V system). More sun, more amps. Less sun, fewer amps - but all at 18V. That's simplistic, but about how it works.
If you have two such panels in parallel the Vmp will be 18V. The MPPT reg will try to holding the combined panel voltage at 18V. If the panels are equally lit, the amps into the reg will be double what one panel could provide.
If one of those panels is shaded, then there are two possibilities.
1 If you have no blocking diodes the MPPT reg will try to hold the panel voltage at Vmp, 18V. Some of the resulting current from the lit panel will backfeed into the shaded panel and be dispersed as heat in the shaded panel. THE REMAINDER will go to the reg and charge the battery.
2 If you DO have blocking diodes the MPPT reg will try to hold the panel voltage at Vmp, 18V. The lit panel cannot backfeed to the shaded panel, so ALL ITS OUTPUT will go to the reg and charge the battery. That is what you want.
Both of these scenarios assume that there is enough sun to allow the MPPT reg to keep the panels at their Vmp and take the resulting current.
If there is not enough sunlight on one or both panels to keep the voltage up to Vmp, then the system will be unable to track the maximum power point and will revert to a less efficient method. What that is depends on the design of the reg.
Cheers