Perhaps an overview may be helpful to some.
1) Caravans are fitted with multiple 230v power outlets each of which may accomodate appliances rated at up to 10 Amps. Accordingly, it is possible to attempt to draw excessive current and the caravan is fitted with circuit breaker(s) which will limit that current to 15 Amps. The caravan now effectively becomes an 'appliance' that may attempt to draw 15A from its supply source.
2) Because of the above, the caravan input is fitted with 15A rated plugs and cable, and the caravan parks have accomodating 15A power outlets.
Even if, on occasion, you intend to only draw less than the maximum of 15A, say only a few Amps to operate the battery charger or fridge, the possibility exists to draw more and if you connect the van to a 10A power outlet you may overload the outlet and the building cable supplying it. Hence the regulations prohibiting this action.
3) Some may argue that the building cable and circuit breaker are rated at 16 or 20 Amps and therefore capable of supplying the van with 15A. However this makes no regard for other outlets and connected appliances within the building on the same circuit and contributing to the total load. A dedicated 15A rated power outlet has its own exclusive cable and circuit breaker and can support the 15A load.
4) The regulations relating to these electrical installations take into regard the possibilities that may cause damage or injury and are composed accordingly.
5) Modifying or constructing the connecting extension cord to allow the 15A caravan to be connected to a 10A rated power outlet is not lawful. It may not be specifically dangerous if used within limitations but may cause injury or fire if used beyond those limitations, either inadvertently or intentionally.
6) The only lawful and safe arrangement is to connect only to a dedicated 15A power outlet or incorporate a current limiting device such as an "Ampfibian" or similar which effectively makes the van a '10 Amp appliance'.
7) Much the same applies when connecting a portable generator to the caravan's input. If the generator is fitted with 15A rated outlet sockets then there is no problem. If however the generator has only 10A sockets then the correct procedure would be to use current limiting as in 6) above.
Even though the generator is fitted with overload protection the manufacturer may consider that, as its output is limited, there is no reason to create a false impression by using 'oversized' 15A output sockets.