why is bigger better

Submitted: Thursday, Oct 28, 2004 at 19:00
ThreadID: 17393 Views:3408 Replies:11 FollowUps:24
This Thread has been Archived
im still confused over thicker wire is better when it comes to fridges ect.
ok i know 6 mm is a good start when running wire from the front to back of a vehicle.
now the bit i dont get is even if you ran 10mm wire why is it that it only runs through 1 mm of fuse.
im running 8 mm from the baterry to a 40 amp fuse then 8mm to the redarc.
i was bored today so i pulled a 40 amp fuse out to measure it and its 1 mm.
thats all for now thanks
Back Expand Un-Read 0 Moderator

Reply By: Member - Jeff M (WA) - Thursday, Oct 28, 2004 at 19:07

Thursday, Oct 28, 2004 at 19:07
Yeah I can understand where you're confusion is comming from. But it's all about length. It's just like using a garden hose sprayer. The further your spray the water the more it disperses. If you hold the hose right up to your pavers it'll clean em' good, if you try to clean them from 10m away you will have lost pressure.

The further the voltage has to go down the wire the more "loss" you have. When you start taking a substantial load off that long wire (ie a fridge at 4 amps) then you get what is called "voltage drop" because of the shear distance the cable is unable to provide the power correctly to the appliance because too much of it is getting dispersed along the way.
A fuse is only a 1 cm long, the voltage drop over that distance would be minimal. As long as that peice of wire can handle the current being drawn through it it should make very little difference to the overal picture.
Hope that makes sense...
AnswerID: 82133

Follow Up By: mr diamond - Thursday, Oct 28, 2004 at 19:21

Thursday, Oct 28, 2004 at 19:21
thats sort of makes sense but if you have a big hose and squish the hose to 1/8th its size at the tap end wont you still get a dribble out of the other end?
0
FollowupID: 341260

Follow Up By: Member - Jeff M (WA) - Thursday, Oct 28, 2004 at 19:27

Thursday, Oct 28, 2004 at 19:27
Yeah that's where it get's wierd I spose.
The thin wire can carry just as much current as what you would be drawing from you big wire, the big wire has the capacity to handle a hell of a lot more than what you are going to put through it. It's more down to a kind of insulation. I guess if you where to put the nozzle of the hose into a rectangle peice of metal that lead all the way over to where you wanted to clean them it would not be as good as standing right there, but you would lose a lot less water out the sides.
The thicker wire will loose less of the power over the longer distance. When you wire up your stereo at home you could use fuse wire if you wanted to, but the speakers will sound heaps better if you use the thickest wire you can find. Less noise, less loss etc.
When you rig up antennas for Two ways and CB's you can use your normal RG58 coax but over long runs or up tall antenna masts you lose output power through the cable, if you get military grade really thick coax cable with the same impedence you won't lose so much TX power over the same distance.
0
FollowupID: 341263

Follow Up By: Member - Chris M (QLD) - Friday, Oct 29, 2004 at 08:13

Friday, Oct 29, 2004 at 08:13
Agree with Jeff.

But you can still go over the top as well and have the same affect over a short distance by using to large a cable as well! So don't go running the spare 130 square mm cable left over from your mates job running temp power to a crane! ;-)
0
FollowupID: 341354

Reply By: Lone Wolf - Thursday, Oct 28, 2004 at 19:32

Thursday, Oct 28, 2004 at 19:32
Damn good analogy!!

Now, the fuse is what............ 15 - 20 mm. long of wire? That is the toughest part for the power to go thru.

The rest of the wire will let the power just sort of dawdle thru, without getting all squashed up.

This may make it easier.............

You have BIG power stations in the Yallourn Valley, and your light switch at home. You flick the switch to ON. Now, contrary to popular belief, all those little electrons just don't go hurtling down from Yallourn to your house. They dance around, like a moving sea of electrons could take up to a year to get to your house!! You'll get the bill quicker than that!!

So, the electrons need HEAPS of room to FREELY MOVE AROUND, and they are not like water, and come out the end of the hose all sequential like.

Hope this helps.

Cheers

Wolfie
AnswerID: 82136

Follow Up By: mr diamond - Thursday, Oct 28, 2004 at 20:00

Thursday, Oct 28, 2004 at 20:00
its all to confusing water/electrons/hoses/power stations.lol
i think ill just remove the fuse box to save my sanity.
0
FollowupID: 341271

Reply By: GOB & denny vic member - Thursday, Oct 28, 2004 at 21:04

Thursday, Oct 28, 2004 at 21:04
just to add more confusion if you heat the wire anyway it will cause more resistance and more voltage drop
lol

steve
AnswerID: 82163

Follow Up By: Member - Jeff M (WA) - Friday, Oct 29, 2004 at 10:53

Friday, Oct 29, 2004 at 10:53
Yeah using too smaller a wire can be a vicous circle as the smaller the wire the hotter the wire get's when running a load through it.
0
FollowupID: 341368

Reply By: GaryInOz (Vic) - Thursday, Oct 28, 2004 at 21:20

Thursday, Oct 28, 2004 at 21:20
Diamond,

I started typing out a reply but it all got too complicated, so here is my version of a simple answer.

It is a bit like driving along on a muddy track, there is a bit more resistance than on the bitumen but you can manage it easily. Think of this part as the heavy guage wire going to your fridge.

OK now the going gets a bit heavier and you hit a bog about 1' deep but only 2' long. You feel it but it really doesn't slow you down that much. This is the situation with the fuse, more resistance but short enough that it doesn't lose too much voltage across it.

Taking it one step further if your wire going to the fridge was the same size as your fuse, can you guess how long that 1' deep bog is now??? Lead wellie time....big time voltage drop.

The difference between your wellie position and your forward progress represents the resistance of the road surface, a bit like the resistance to voltage along a length of cable, the thinner the cable (deeper the bog) the more resistance to forward progress (voltage) there is.

Before all the physics professors get on my case I know it is not stictly a good example, just a representation in a way that may make a bit more sense to those with no electronics background.
AnswerID: 82167

Follow Up By: Ian from Thermoguard Instruments - Thursday, Oct 28, 2004 at 22:36

Thursday, Oct 28, 2004 at 22:36
Bulk Applause, Gary!
I also thought about replying but couldn't get beyond my engineering mindset and it all started to sound too bl**dy complicated!

I've toyed with the idea of doing a bit of TAFE tutoring as we travel around this wide, brown land - if I ever score a job teaching lads about electrickery and ergertrons, may I use you excellent example???
0
FollowupID: 341316

Follow Up By: Lone Wolf - Friday, Oct 29, 2004 at 07:26

Friday, Oct 29, 2004 at 07:26
Well Gary, I'm impressed!!

That was the best analogy I've ever heard.

We are going to place you in the EO hall of fame............ the Dr. Zeuss of Billy's Bike is stuck in an electron field!!!!

Good Work.......

Wolfie
0
FollowupID: 341339

Reply By: Member - John (Vic) - Thursday, Oct 28, 2004 at 22:15

Thursday, Oct 28, 2004 at 22:15
Jim don't worry about it, Just accept that this is what happens and you need a big wire, the bigger the better.
VKS737 - Mobile 6352 (Selcall 6352)

Lifetime Member
My Profile  Send Message

AnswerID: 82176

Follow Up By: Mad Dog (Victoria) - Thursday, Oct 28, 2004 at 22:19

Thursday, Oct 28, 2004 at 22:19
Yes John but Jim is a "thinking man" He likes to ponder these little mysteries over a drink or two or three :)
0
FollowupID: 341307

Follow Up By: Member - John (Vic) - Thursday, Oct 28, 2004 at 22:35

Thursday, Oct 28, 2004 at 22:35
I can just picture poor old Jim with his head between his hands bent over and moaning out loud 'Oh I am sooooo confused"

The bigger the better, thats what my girlfriends always say. LOL
VKS737 - Mobile 6352 (Selcall 6352)

Lifetime Member
My Profile  Send Message

0
FollowupID: 341315

Follow Up By: Nudenut - Friday, Oct 29, 2004 at 07:50

Friday, Oct 29, 2004 at 07:50
John, bigger mens less resistance for electrical.....but as for what your lady says cant be right....bigger must mean more resistance
0
FollowupID: 341348

Reply By: drivesafe - Thursday, Oct 28, 2004 at 22:21

Thursday, Oct 28, 2004 at 22:21
GaryInOz, a good reply and definitely a different way of putting it.
Cheers
AnswerID: 82178

Reply By: Neil & Lynne - Friday, Oct 29, 2004 at 00:13

Friday, Oct 29, 2004 at 00:13
That was a well described analogy to explain resistance. Now, can someone answer this.....if you were to take a 6mm multistrand wire and a 6mm single strand wire, which one will carry current more efficiently, with less resistance?
OK. I have it on good authority it is the multistrand, but I have no idea why?
Anyone????

Neil.
AnswerID: 82193

Follow Up By: Member - John (Vic) - Friday, Oct 29, 2004 at 00:33

Friday, Oct 29, 2004 at 00:33
Because it does, Jeez you blokes are losing sleep over nothing.
It just does don't worry about the detail.

I have no idea either.
VKS737 - Mobile 6352 (Selcall 6352)

Lifetime Member
My Profile  Send Message

0
FollowupID: 341330

Follow Up By: Ian from Thermoguard Instruments - Friday, Oct 29, 2004 at 00:34

Friday, Oct 29, 2004 at 00:34
Dear me , Neil, it's getting very late for questions like this but... it's all to do with the cross-sectional area (CSA) of the copper conductors.

I'll try to put my brain into gear tomorrow and explain it in more detail but.. a large part of the problem is this weird automotive electrical practice of describing wires by their overall diameter (including insulation!) rather than the CSA of the actual copper conductors.

Get back to you soon.
0
FollowupID: 341331

Follow Up By: Member - John (Vic) - Friday, Oct 29, 2004 at 00:47

Friday, Oct 29, 2004 at 00:47
Actually Ian I didn't think that the Automotive industry did talk in dia as opposed to CSA.
I thought that wire was expressed as CSA regardless of the application.
VKS737 - Mobile 6352 (Selcall 6352)

Lifetime Member
My Profile  Send Message

0
FollowupID: 341332

Follow Up By: Ian from Thermoguard Instruments - Friday, Oct 29, 2004 at 01:02

Friday, Oct 29, 2004 at 01:02
Sorry, John, but , yes they do (for some strange reason). Walk into any hardware shop, Supercheap Auto, K-mart auto section, etc. and you will find rolls of automotive wire labelled "3mm", "4 mm" etc. This has no direct relation to it's CSA. I'll dig out my "equivalents" list tomorrow and post it, OK?
0
FollowupID: 341333

Follow Up By: Tim - Friday, Oct 29, 2004 at 01:37

Friday, Oct 29, 2004 at 01:37
Neil and Lynne
I would have a guess that it may be for 2 reasons.
1. The multistrand has more surface area (not CSA but the actual surface area of each strand) which would allow more cooling than solid therefore has a better temperature co-efficent.
2. This could be a bit far fetched but it may also be that when this theory was tested, the solid conductor was touching the multi meter lead and the multi strand was wrapped around the lead which would give more surface area and less resisitance at that joint.

There would be very little in it and your most meters would struggle to seperate them unless it was a very long run.
Either way, solid conductors should not be installed in vehicles or in industrial situations because with constant vibrations they will eventually break.

Tim
0
FollowupID: 341334

Follow Up By: V8troopie - Friday, Oct 29, 2004 at 01:47

Friday, Oct 29, 2004 at 01:47
6mm multistrand against 6mm single strand? Is that a trick question?

The 6mm should actually read 6 sq mm to be correct. Dumb people labelling the shop stock obviously don't know about this.

Now, 6 sq mm = 6 sq mm, regardless if its single or multi strand.

So, for DC, there is no difference in current carrying capacity.

Ever since we got rid of the old wire gauge sizes and replaced it with a much more logical and simpler system people seem to do their very best to confuse things.

In an ideal world:

Insulated wire is labelled by the total cross sectional area. It may also indicate how many strands of what size to judge its flexibility.

Enamelled magnet winding wire or plain bare copper wire is labelled by its diameter.

Klaus
0
FollowupID: 341335

Follow Up By: MrBitchi - Friday, Oct 29, 2004 at 08:25

Friday, Oct 29, 2004 at 08:25
Think that applies to AC current, not DC. AC current uses a phenomenon called "Skin Effect" where the current actually flows on the surface (skin) of the conductor. Multi strand cable has more surface area (skin) and can therefore carry more current.
Wow, now my brain aches..... :-(
0
FollowupID: 341355

Follow Up By: GaryInOz (Vic) - Friday, Oct 29, 2004 at 08:52

Friday, Oct 29, 2004 at 08:52
MrBitchi, you are correct, but only for radio frequencies (no need for transmission line theory...). For the most part our houses and workplaces are wired up for 240 volts in single core cable.

6 sq mm = 6 sq mm, like one foot = 12 inches when you are talking about DC up to the higher audio frquencies. Anyone that tries to sell "special" wire is full of BS. for all intents and purposes they are the same, but you would only use single core cable in fixed situations not subject to vibration.

Leads to another question: Do they use multi strand cable in house wiring in New Zealand and Japan???? ;-)
0
FollowupID: 341357

Follow Up By: MrBitchi - Friday, Oct 29, 2004 at 09:00

Friday, Oct 29, 2004 at 09:00
GaryInOz,
Must admit all this theory stuff was a few years back.... We're all geting older :-(
0
FollowupID: 341359

Reply By: MrBitchi - Friday, Oct 29, 2004 at 08:39

Friday, Oct 29, 2004 at 08:39
Smoke.
Most people think electricity is a flow of electrons in a piece of wire which cause things to work by their electromagnetic properties (electric motors) or the effect of heat due to resistance (Light bulb).
This is not in fact the case.
Electricity is in fact smoke. All those wires you see around the places are actually little pipes carrying smoke of various colours.
When all is good there are no leaks and all the smoke stays in the wire (pipe) and things work properly.
When something goes wrong, however, the pipe gets broken and the smoke escapes.
The amount of smoke is directly proportional to the cost of the repair. A small amount of clean white nearly odorless smoke will be relatively cheap to fix, whereas a large amount of dirty brown smoke, usually accompanied by what is technically called a “dirty brown smell”, will usually cost you a second mortgage to rectify.
So make sure that all your taps (terminals) are tight and clean, your pipes (wires) are in good condition and free from cuts and corrosion, and have a smoke free day.
Cheers.....
AnswerID: 82207

Follow Up By: GaryInOz (Vic) - Friday, Oct 29, 2004 at 08:53

Friday, Oct 29, 2004 at 08:53
Priceless!!!!
0
FollowupID: 341358

Reply By: Redeye - Friday, Oct 29, 2004 at 09:32

Friday, Oct 29, 2004 at 09:32
Well all,

The diameter of the wire determines the resistance of the wire per meter. A thick diameter has less resistance per meter.

Then look at the equation of current (I) = voltage(E)/resistance(R).

From this the less resistance in the circuit the more current will be available for the fridge.

Example:

Average Waeco draws 3.5 amps (approx) so has a resistance of R=E/I = 3.4 ohms
If the resistance of your wiring was 1 ohm it would mean the fridge would only have a supply voltage of 9.27 volts with a battery if 12 volts

AND

8.88 volts when the battery falls to 11.5 volts.

I realise that the resistance of the wiring is less than one ohm but hope this explains why you require the thicker wiring when considering the voltage of a battery can decline when not being charged.

Redeye

AnswerID: 82215

Reply By: Member - Collyn R (WA) - Friday, Oct 29, 2004 at 12:23

Friday, Oct 29, 2004 at 12:23
This thread may hopefully solve a number of electrical problems - particularly relating to 12 volt fridges.

Materials such as copper, that allow electricity to flow, are not perfect conductors. To varying degrees they oppose that flow. This opposition causes that conductor to heat up and that energy is lost.

The smaller the cross sectional area of the conductor, and the greater its length, the larger the loss.

A fuse has very small cross-sectional area, but of such short length, that the loss is not that great. The older-type glass fuses however can cause problems as the contact between the fuse and the fuseholder tends to corrode.

The major concern however is that raised by Klaus and others - and that relates to cable 'rating' standards.

Electrical appliance makers worldwide (except the USA) specify cable in terms of its cross sectional area (in sq. mm.). But when you set out to buy the (say) 4.0 or 6.0 sq mm cable called for, what you will almost certainly be sold is 4.0 or 6.0 mm auto cable.

For reasons that defy sanity, auto cable is sold with similar 'numbering' (eg. 3.0 mm. 4.0 mm, 6.0 mm) but that measurement is of its overall diameter - including the insulation.

The appliance maker logically specifies the cross sectional area of the copper that carries the current.

The auto cable maker specifies the size of the hole the cable can be pushed through - and uses the same bloody numbering!

This is not an error made by auto parts staff. It is the way the stuff is rated by its makers. I have however yet to find a single person in an auto parats store who is even vaguely aware of this matter - let alone its consequences.

Is those consequences serious?

You bet they are!

Because the ratio of copper/insulation varies from auto cable maker to auto cable maker there is no such thing as a universal comparison table.

Roughly though (and using the mosty common sizes available in Australia):

3.00 mm auto cable is about 1. sq mm.

4.00 mm auto cable is 1.8-2.0 sq mm.

6.00 mm auto cable is typically a tad under 4.6 sq mm.

As a very commonly used size is 4 mm, a HUGE number of fridges (probably most) are connected via cable that is, at best 50% undersized, and in many cases close to 60% undersized.

Using the correct size cable makes an enormous difference to performance.

Be aware also that the so-called 'current rating' (like 30 amp) is simply a measure of the current that cable can carry before the insulation melts. It bears no relationship to voltage drop.

The above affects a huge number of RV electrical installations including many done professionally.

I first raised this issue in an early edition of my book 'Motorhome Electrics' - I thought then that it was of concern, but only limited concern. It has turned out be a huge issue worldwide (except in the USA where a different cable rating system is used) - and a huge number of RVs are affected.

I am currently finishing a 'Guide to Solar' for publication on this Forum - and I have covered this issue also in this.

Re single/multi-strand cable: multi-strand is necessary for anything that moves as it is very much more flexible. The current carrying capacity at dc and low frequency ac (such as mains voltage) is virtually identical, but at radio type frequencies and above, the ac current tends to travel on the outer surface of the copper hence multi-strand is used because of it massively larger surface area.
Trust this helps
Collyn Rivers
AnswerID: 82231

Follow Up By: Ian from Thermoguard Instruments - Friday, Oct 29, 2004 at 12:55

Friday, Oct 29, 2004 at 12:55
Good one, Collyn! This very well explains the CSA Vs stupid automotive cable 'overall diameter' marking issue I was struggling with in a red-wine-induced haze, late last evening.
0
FollowupID: 341379

Follow Up By: G.T. - Monday, Nov 01, 2004 at 17:50

Monday, Nov 01, 2004 at 17:50
Given that 6.00mm auto cable is approx 4.6 sq mm, what size auto cable do you use to get 6.00 sq mm ? Thanks in advance. Regards G.T.
0
FollowupID: 341610

Follow Up By: G.T. - Monday, Nov 01, 2004 at 17:52

Monday, Nov 01, 2004 at 17:52
Sorry my follow up should have been addressed to Collyn. Regards G.T.
0
FollowupID: 341611

Follow Up By: Ian from Thermoguard Instruments - Monday, Nov 01, 2004 at 23:19

Monday, Nov 01, 2004 at 23:19
Hi GT,

I don't have a precise answer to hand, but you might also like to look at this Dick Smith Electronics page. It is a straight forward way to size cables for 12Vdc automotive/marine applications.

Hope this helps.
Ian
0
FollowupID: 341716

Reply By: Member - Collyn R (WA) - Tuesday, Nov 02, 2004 at 13:18

Tuesday, Nov 02, 2004 at 13:18
GT

There is no auto cable that approximates 6.0 sq mm. The closest is so-called '8 gauge'. This is an unusual size in that it's about the same cross-sectional area in virtually all rating systems!

You may find it called 8 B&S (and I bought 60 metres of it labelled exactly that from Rheen Auto Electrics in Broome, yesterday). It's a tad over 8 sq mm. The American AWG 8 gauge is virtually identical. And a few auto parts stores know it as 8 mm auto cable.

It's a bit overkill - but for fridge wiring etc nothing succeeds like excess!
Most auto-electricians will sell you a length (about $2-$3 a metre but it's worth every cent).

Trust this helps
Collyn Rivers
AnswerID: 82721