Safety Alert
DATE: 20/10/04
INITIATED BY: Dave Hall
DEPARTMENT: EHS Department
INFORMATION TO BE COMMUNICATED:
Department of Consumer and Employment Protection
Government of Western Australia
Energy Safety Division
Public Safety Alert
Warning on the use of
inverters
Recently, it has been bought to the attention of Energy Safety that there are some
portable
inverters with 240 volt ac output and 12 volt or 24 volt dc (or similar) input that,
under certain conditions, may develop a hazardous voltage between the battery
terminals and the exposed metal of appliances or the inverter.
There are reports of accidents and a fatality with these
inverters, possibly due to these
conditions and how they were used. Where the inverter design does not ensure
appropriate isolation between the battery supply and the 240 volt output supply for an
electrical appliance, there is the possibility that under a fault condition, the battery
terminal or any metal connected to the battery could become energised to a dangerous
level.
Energy Safety is concerned that the use of some
inverters may cause the operator to
be at risk.
Inverters have been available for a number of years and are commonly used in vehicles
and boats and in recreational applications. The use of the
inverters has been allowed
on construction and demolition sites since the publication of the 2003 edition of
AS/NZS 3012.
The Standards Committee responsible for AS/NZS 3012 has decided that, as no
standard exists for
inverters, requirements will be developed for
inverters used on
construction and demolition sites. A review has commenced and will include the
opportunity for public comment. This review particularly concerns the type of inverter
with interconnections between the battery and the 240 volt output, and will consider all
types of
inverters. Under consideration are appropriate insulation requirements,
equipotential bonding of all exposed metal and the battery, polarisation of the output
and the need for RCD protection. It is proposed that units suitable for construction work
be appropriately marked. Tests for verification and tagging will also be proposed.
Until this review is complete, it is the position of the committee that
inverters should not
to be used for construction and demolition work. The committee has requested that
regulators advise stakeholders as a matter of urgency. Energy Safety endorses this
direction until a solution is provided to this problem and will also consider the outcome
for application in other than construction and demolition site environments.
In the interim period, other users of
inverters are urged to be cautious when selecting
an inverter, especially those with warnings such as “Improper use can result in fatal
voltages on the battery terminals, failure of the inverter and/or fire”. Guidance should be
obtained from the manufacturer or supplier to enable the selection of a safe type for the
intended use.
Issued: July 2004