Wok
Hello,
I am looking for Brands and/or Sources of manual resettable circuit breakers to 50A DC........any suggestions please?
Thanks
Reply By: davidta - Saturday, Nov 20, 2004 at 13:55
Saturday, Nov 20, 2004 at 13:55
Hi
Jaycar has them in 80A & 100A.
AnswerID:
85153
Follow Up By: Wok - Saturday, Nov 20, 2004 at 14:48
Saturday, Nov 20, 2004 at 14:48
Thanks...I see them!
FollowupID:
343763
Follow Up By: Bonz (Vic) - Saturday, Nov 20, 2004 at 18:41
Saturday, Nov 20, 2004 at 18:41
what're they worth each? if you happen to know?
Thanx
FollowupID:
343777
Follow Up By: Wok - Saturday, Nov 20, 2004 at 20:14
Saturday, Nov 20, 2004 at 20:14
Bonz,
Both are $22.95 each
SF-2265 : 70A [not 80A]
SF-2266 : 100A
There is a differance in trip times
rgds
FollowupID:
343789
Reply By: theshadows - Saturday, Nov 20, 2004 at 13:56
Saturday, Nov 20, 2004 at 13:56
order them from Ashdown at northgate QLD. you can order on line or telephone sale them.
50 amp a bit large you might want to go to caterpiller type manual breaaker for that . other than that ashdown have blade type that replace nomal blade fuses.
It cost e a fortune but i never have to worry about finding the blown fuse again . just press a button and its reset.The only problem is on long corragations I have had 2 pop on me.
shadow
AnswerID:
85154
Follow Up By: Wok - Saturday, Nov 20, 2004 at 14:51
Saturday, Nov 20, 2004 at 14:51
Shadow,
What do you mean by 'pop'?...Did they fail or trigger wrongly?
Thanks
FollowupID:
343764
Follow Up By: theshadows - Saturday, Nov 20, 2004 at 15:08
Saturday, Nov 20, 2004 at 15:08
triggered wrongly. I wa wondering why my AC dropped out then latter in the day noticed that my speedo failed.
Both time the breakers had triggered.Mind you it was 230 km of hard QLD corrigation .
shadow
FollowupID:
343765
Reply By: Solarpower - Saturday, Nov 20, 2004 at 16:26
Saturday, Nov 20, 2004 at 16:26
Ashdowns mainly have dubious to poor quality components now as they have lost the agency for quality brands like Hella. Ashdown is just another REPCO company (Rip Every Poor Customer Off)
Ingrams have branches all over Australia and sell quality brands like Hella and Narva and you can buy with confidence from them.
AnswerID:
85162
Follow Up By: Member - Collyn R (WA) - Saturday, Nov 20, 2004 at 16:39
Saturday, Nov 20, 2004 at 16:39
For really good quality Outback Marine in Qld take some beating.
As with most stuff electrical beware of cheap circuit breakers as they tend to be very temperature sensitive.
Collyn Rivers
FollowupID:
343769
Follow Up By: Bonz (Vic) - Saturday, Nov 20, 2004 at 18:52
Saturday, Nov 20, 2004 at 18:52
Collyn, I must say your knowledge and opinions are excellent, I have learnt a great deal from your posts. Keep it up mate!
FollowupID:
343778
Follow Up By: Wok - Saturday, Nov 20, 2004 at 20:17
Saturday, Nov 20, 2004 at 20:17
Collyn,
Thank you...that would be the Blue Sea units.
Had a look at the Sterling website re: dc-dc type battery chargers,,,they certainly have a long winded way of describing their product?
rgds
FollowupID:
343790
Follow Up By: Wok - Saturday, Nov 20, 2004 at 20:21
Saturday, Nov 20, 2004 at 20:21
Solarpower,
I agree about Ashdowns, Coventry is my local choice, must check if Ingrams is in
Brisbane.
Thanks
FollowupID:
343791
Reply By: Member - Collyn R (WA) - Sunday, Nov 21, 2004 at 10:03
Sunday, Nov 21, 2004 at 10:03
Wok/Bonz
The best circuit breakers are marine units approved by UL, CSA, and Loyds. I'd recommend Heinemann, ETA and Carling. Blue Seas Ok but would prefer the others.
Specify as follows:
Conductor size (in sq mm) Circuit Breaker Rating
1.5 8 amps
2.5 16 amps
4.0 20 amps
6.0 30 amps
10 40 amps
16 60 amps
25 80 amps
35 100 amps
50 120 amps
DO note the above conductor sizes are sq mm (ie ISO) - they are not auto cable.
Further, circuit breakers protect feed cables against a short to earth. They should therefore be located as close to the battery as possible.
You can if you wish pick the circuit breaker to match the load current - but this is not essential. If you specify as shown above, the circuit breaker will not need to be changed if you make any additions to the load.
Re Sterling: I am aware of the latest products - but, as with others, I am puzzled about his very vocal and seemingly illogical dislike of AGM batteries.
Trust this helps
Collyn Rivers
AnswerID:
85232