Friday, Nov 16, 2007 at 20:39
Thanks Mike
I am measuring with a dick smith multimeter. This thermocouple is made with the insulated positive wire running through the middle of a copper tube with the copper tube acting as the earth. According to web info this type typically output 14 - 30 millivolts). I place the probes of the meter on
the tip of the thermocouple (+) which makes physical contact with the electromagnet in the gas safety valve and earth to the copper tube itself. I have experimented by repositioning the probe in the flame to a slightly different position and am now achieving 16.9 - 17 millivolts. I am using the 200m setting on the meter and have tried several positions, pressures etc and am getting a very consistent reading. Since moving the probe and obtaining a better voltage I now find the electromagnet is now much happier to
seat. I would like to have a little more voltage but will probably be happy with the result as is. The thermostat is working with the gas flame reducing to 'pilot' at 0.2 C.
The pilot flame is quite small so I am now worried about it blowing out while in
the pilot position. Do you know if this can be increased (slightly would do). I notice a small screw on the side of the thermostat and wonder if it may adjust
the pilot).I also note that the later models ie the f400 have less slots at the rear of the unit near where the flame is located and am wondering if fitting a plate at the rear to reduce ventilation (around the flame only) would help in avoiding
the pilot blowing out. Comments would be welcome.
regards Kc
FollowupID:
535216