G'day all, can someone please tell me if a honda eu10 genie will run my ctek 25000 charger with some power to spare for lights ect around camp. I can't seem to to find the power needed to run the ctek.
Back Expand Un-Read 0 Moderator

Reply By: Member - Tony (ACT) - Tuesday, Dec 29, 2009 at 06:09

Tuesday, Dec 29, 2009 at 06:09
Yes it will do the job fine, I had a ctek 25 for a short time, change it to a selectro 30 amp charger as it was quicker to bring battries up to float,

4 hours agaunst the ctek around 7 hrs. Less fuel.
AnswerID: 396716

Reply By: Bonz (Vic) - Tuesday, Dec 29, 2009 at 08:04

Tuesday, Dec 29, 2009 at 08:04
The power would be something like:

25 (amps) * 14 (volts) * 80% (efficiency)

So about 440w or about half what your EU10 puts out.

Shouldnt be a drama
.
Time is an illusion produced by the passage of history
.

Lifetime Member
My Profile  My Blog  My Position  Send Message
Moderator

AnswerID: 396729

Reply By: Member - Andrew (QLD) - Tuesday, Dec 29, 2009 at 08:17

Tuesday, Dec 29, 2009 at 08:17
In the manual, they list the mains current draw as 2.9A rms at full charging current ..... equates to just less than 700W.

Hope that helps.

Andrew
AnswerID: 396731

Follow Up By:- Tuesday, Dec 29, 2009 at 10:52

Tuesday, Dec 29, 2009 at 10:52
Ctek recommend the size of the generator to at least be double the size of the charger. The MULTI XS 25000 (300W) needs at least 650VA to function correctly.

Looking at this, it becomes apparent that the combined efficiency factor and power factors is 0.46.

Assuming the following:
P/F generator: 0.8
P/F charger: 0.9 (as PFC is stipulated by standard)
The AC/DC conversion efficiency is allowed to go as low as 0.63 under this scenario.

The end result is, that for every Ah the charger puts into the battery, it draws the equivalent of 1.6Ah from its source.
During times of peak charging current, the generator fuse gets to see a current 2.17 times higher than the maximum charger wattage would suggest - 2.7A versus 1.25A.

In a nutshell, as long as your generator is rated higher than 650VA, and the output fuse >2.7A you'll be able to run your charger off the gennie. It should be easy for you to work out the spare capacity left to run additional loads at the same time. Note that the maximum current draw by the charger only happens for a fraction of the total recharging time, depending on the DOD of the connected battery.

Best regards, batterymeister
0
FollowupID: 665490

Reply By: Member - Ian W (NSW) - Tuesday, Dec 29, 2009 at 09:58

Tuesday, Dec 29, 2009 at 09:58
I run a CTek 25 off a EU10.

When charging I used to run all I could off 240V whilst the generator was running. Seldom need it now I've been able to fit solar.
AnswerID: 396740

Reply By: Haddo - Tuesday, Dec 29, 2009 at 10:31

Tuesday, Dec 29, 2009 at 10:31
Thanks everyone, thats solved my query. I think i'll order new genie today. Cheers !
AnswerID: 396751

Follow Up By: murranji - Wednesday, Dec 30, 2009 at 17:22

Wednesday, Dec 30, 2009 at 17:22
Reading all of the above will my Honda 650 generator run my cetek 25000 with no problems to charge ? I beleived it would all work O K to charge quickly in the bush..Have I made a blunder...
0
FollowupID: 665701

Reply By: Matt(WA) - Wednesday, Dec 30, 2009 at 20:14

Wednesday, Dec 30, 2009 at 20:14
I run a ctek 25000 off a honda gx500 2 stroke. 500w gen and it runs well