Solar controllers and batteries connection

Hi all,

I have a small question to you solar gurus :).
My father-in-law installed a few solar panels for the camping car that charge four AGM batteries connected in parallel. This is done by splitting the panels in two groups and by using two Steca PR 3030 controllers connected in parallel (yep here in Switzerland we don’t have so much sun and the whole installation can easily go over 30A on sunny days).
I am not an AGM charging specialist, but this seems a bit fishy to me. Can two PR controllers be connected in parallel on batteries? My feeling is to have each controller manage two batteries and connect them in parallel at the load outputs.
But up to now, nothing burnt, so he cannot be completely wrong :).

Any thoughts?
Back Expand Un-Read 0 Moderator

Reply By: Member - John and Val - Monday, Oct 04, 2010 at 08:05

Monday, Oct 04, 2010 at 08:05
Hi glandvador,

Good to hear from the other side of the world!

This must be a big solar array. I doubt that there is any reason not to leave all batteries in parallel, though there might be some advantage in connecting as you suggest, two parallel pairs, each pair connected to the load through its own controller. That way, if one battery got tired it wouldn't affect the other pair.

The only disadvantage I can see to the present arrangement is that there might be some undesirable interaction between the controllers when they are lightly loaded, ie when the batteries are fully charged.

Think I'd be asking the manufacturer for a definitive answer.

Cheers

John
J and V
"Not everything that can be counted counts, and not everything that counts can be counted."
- Albert Einstein

Lifetime Member
My Profile  My Blog  Send Message

AnswerID: 432073

Reply By: Battery Value Pty Ltd - Monday, Oct 04, 2010 at 09:46

Monday, Oct 04, 2010 at 09:46
glandvador,

the stecas are common positive regulators.
This means there's a permanent connection between battery positive and load positive.
And while the battery's sitting above the low voltage cutoff, the electronic switches which are in the negative leg between the load and the battery are closed.
So it doesn't matter which way you make a parallel connection. It can be done on the battery side, or on the load side.

But there's more to it:

in case one of the four batteries develops a fault (shorting out of a cell), this battery then discharges the other battery which is directly wired in parallel.
But it'll also discharge the other two batteries if they were all wired in parallel.

On the other hand, if the two battery pairs are wired in parallel via the load terminals, then this would effectively prevent the 'good' pair from being drained to the same voltage of around 11.4V. Instead, it'll only be drained to 11.8V.
That's because the voltage differential between the good and bad pairs is reduced by the forward voltage drop of the drain-source diode which is an integral part of the electronic switch (power MOSFET). Sorry if I've confused you with techno speak.

To sum it up.
This can be done either way, but connecting via the load terminals has a small advantage which becomes relevant if one battery develops a fault.

grüezi
AnswerID: 432078

Reply By: glandvador - Tuesday, Oct 05, 2010 at 03:59

Tuesday, Oct 05, 2010 at 03:59
Thanks,

Yes, it is a pretty big array. It's needed on bad days :)

For the light loaded controllers, I think this is pretty much what he observes,
one shows 13.8V and the other 14.X. When charging batteries, they both show the same values.

I will motivate him to change the connections on batteries. Some fun in perspective :)

Best regards,
Glandvador.