Hi Peter,
yes, the transformer needs to come up with 306VA in this case, so you're right 300VA means the stepdown won't quite make it to 204V. Instead it'll settle a touch higher, meaning the appliance will see a slightly higher wattage than the 1730W.
But looking at the gennies specs, this is already exceeding its rated output power, so the 300VA autotransformer isn't big enough to bring the 2400W load down to within the gennies power band.
The 1800W inverter should be fine with it for a few minutes though.
Of course, lower wattage appliances as suggested by Ozhumvee are definitely the easy way out, just what I would do.
Rosiebear:
you're right, after reading the operator's manual it looks like this gennie doesn't need a sync signal as such, as it derives the phase angle information from the parallel output configuration itself.
This opens the door to some experimenting using
inverters.
But looking at the cost of the components involved - I personally wouldn't risk it.
Bob:
yes, seeing how the piggy backed power socket is connected to both generators' outputs, it's a no-brainer to treat these wires with respect as they're indeed not just low voltage signal wires.
cheers, Peter